Odd request
Hello gentlemen
I recently retired but still work sort of as a consultant for my last employer.
they called me to figure out some wiring. I met with the foreman and the home owner. Here is what the homeowner is demanding. Currently he has hot water baseboard and 3 zones. He added central air AC with a 10 kw strip heater. The homeowner only wants to use his current stat for the first floor. It’s a Honeywell Th6. He wants the baseboard and the 10kw heater to come on at the same time on a heat call. That same stat will control the AC also. One more thing he wants a switch on th air handler to turn it off and just use the bbd. I’ll say it for you.. why do you want to do that? Why not put another stat or stat with a sensor for the heat. He doesn’t want another stat. They are using a Taco zone panel. Any ideas would be greatly appreciated. The homeowner has been hard to deal with. Says a guy at work told him to just loop the AHU and the zone panels together. I explained you will buck 2 transformers. He said the stat is battery operated. I had to show him the transformers are in the equipment. Again thank you
Steve
    EdTheHeaterMan Posts: 12,745
    edited January 2025
    the thermostat in question that needs to do 100 different things should operate a relay
    Then you need the relay to have 100 different contacts to do the hundred different things at the same time
    LOL.
    Anyway, if you need to do 3 different things at the same time, you can use a triple pole double throw relay . That way you can turn stuff off and other stuff on with that one thermostat
    jringelhot_roddelcrossv
    EBEBRATT-Ed Posts: 21,026
    Anything can be done with enough relays.
    Put a separate transformer in for the FF stat. Have the stat pull in a couple of heat relays 1 for the baseboard and 1 for the electric strip heat and a cooling relay and a fan relay if you want.
    You can probably use RIB RIBU1C relays. The heat relays pull in from w fan relay from G and cooling from y.
    I don't see any issue.
    bjohnhy
    edited January 2025
    If I get your situation request
    One single stage thermostat will make the TT contacts on the Taco zone panel and the heat in the AHU.
    There also needs to be a manual switch to disable the AHU based on the the customer’s expert inclination and thermodynamic experience.
    Is that about right?
    If yes. I have an idea on how to do this with one DPDT relay like the RIB2401 and a toggle switch
    I can draw the diagram after the Eagles 🦅win this playoff game
    GGross
    edited January 2025
    Assumption about the air handler and air conditioner:
    1. Single stage air conditioner
    2. Legacy Thermostat wiring for air handler / AC = R-G-Y-W-C from thermostat (C is optional to thermostat)
    3. One stage heat on thermostat
    4. There is an existing heat relay on the air handler to operate the resistance heat and blower on a call for heat.
    5. I did not include the outdoor unit for AC since there is no change to that part of the system circuits
    Here is the existing Generic air handler and thermostat on the upper left
    The rest of the diagram shows addition of the RIB2401D and a simple toggle switch.
    The RIB2401D is operated by the white wire from the thermostat. One set of contacts will operate the air handler if the toggle switch is turned on. the other set of contacts on the RIB2401D will operate the zone appropriate baseboard zone on the Taco Zone Panel.
    This will not work on "Communicating" thermostat systems. This will only work on a "Legacy" thermostat wiring
    If you click on the illustration you can zoom in to see the detail
    EASY PEZZY
    GGrossPC7060
    @EdTheHeaterMan
    No taking days off from work just to watch a football game.
    These people need heat LOL😊
    EdTheHeaterManethicalpaulPC7060delcrossv
  • Ed
    We did it exactly as you drew it. It’s up and running. Thank you.
    this was an odd request and the truth finally got out. His wife spilled it. This guy is a real know it all. He decided to install his own baseboard heat. Well, let’s just say he is a lot short throughout the house. Instead of adding baseboard, his solution was to throw 10kw of heat in his air handler.
    I retired 8 months ago. Customers like this make me happy I did. It’s done and the company got paid. Mission accomplished.
    How about Sequan. That man can control the whole game. Great to see a PSU grad do so well
    Thank you
    Steve
    edited January 2025
    He should only need the electric when the outdoor temperature drops below the baseboard's capacity. That's why he needed to have only one thermostat. When people ask "Why 2 thermostats?" he will have to admit his mistake. We can't have that!
    GO BIRDS!
    E L G L E L S or how ever the Mayor spells it today!!!
    mattmia2 Posts: 18,099
    You could definitely have used a 2 stage stat and put the air handler on the second stage in that case.
  • But the customer knows better. "I want what I want when I want it" LOL!!!
    delcrossv
