IBC SFC125 combi 2023 install, poor DHW production;
No experience with the brand. Sounds like it never produced DHW properly.
I'm the third guy. Prior outfit said need new boiler, charged for no solution. Second outfit charged more and said shower valves faulty. When hot water arrives at a faucet I measure a raging peak at 160d that quickly dies down, and settles at 106d.
No AM101 or similar mixing valve present. Guy has a wye strainer on inlet cold. Primary pump does shut down when DHW flow detected. Swap of DHW temperatur sensor no luck. Noticed the guy connected supply/return of system backwards to close tee manifold, but poor DHW happens even with heating zones shut down so hydronic siphon through unlikely(?). I have only one call into tech support, and they seem stretched thin.
Comments
-
does the flow rate drop off also, or just temperature?
Most often there is a small stainer in the unit somewhere that plugs. Maybe in multiple locations.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Has the heat exchanger been de-scaled?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
-
Flow rate doesn’t drop, just temperature.
Installed 2023 and never made DHW correctly. I doubt it’s scaled up but worth a cleanse anyway.
Most of their piping diagrams show a mixing valve on the DHW. I’m thinking that initial shot at hydronic temp level is needed for the inertia of regulated tankless DHW production through the heat exchanger. If regulated through a mixing valve it should sustain at 120 in theory. Hate to do the valve and have it not matter but it’s looking like that might be the problem if it relies on that regulation to pick up heat through the heat exchanger.0 -
-
-
Make sure there is not a crossover somewhere else in the domestic water that's inadvertently mixing down the temp for DHW.
Does the DHW temp drop to 106 as it comes out of combi boiler? or is it just at the faucet? ie, is the temp coming out of the combi 120(or whatever its set to) and then it gets mixed down by the time it hits the faucet?
1 -
As per tech support suggest, I’m test running off the hot side service tap with laundry hose into a bucket with cooking thermometer. Still behaving poorly. Flares at hydronic level 160ish, settles to 106
Framingham, ma.
I’m new to the control, so just getting acquainted. I did get in to change to comfort mode. What else should I be looking at?Good one bjohnny, but I’m test running dedicated out of the unit bottom.
0 -
What is the flowrate? 4 gpm is a bout the max.
If the ground water is super cold that will work against you for sure.
Have you gone into the Installer menu or the Advanced menu to look at the settings?
0 -
Not sure of the exact gpm measure flow rate but I’m simulating about 1.5 gpm into a bucket off of the service outlet. Measuring 46dF incoming cold, so yes it has a lot of ground to cover.
Next move is looking at installer and advanced menu settings to see if they are default or not. Just getting acquainted with control manual on those.
0 -
That "second outfit" was worried about crossover in the shower valve, presumably.
Unless that service tap isolates the house during your test, it could still be cross over, in theory, through back-flow from the house.
When you valve off the DHW at the combi, and turn on a hot water faucet, does it stop completely or do you get persistent slow flow.
What is the temperature setting for DHW?
1 -
-
The SFC has a fast acting cold mix down bypass valve intended to prevent the high temperature burst. The valve mixes down output until the output temperature can be managed by the flame rate. The valve closes down and lets the burner control temperature. I'm guessing the valve is stuck in a mid position.
2 -
the manual also mentions water pressure below 40 psi can cause scalding?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
@kcopp Can't say I've ever seen an sfc125. Thanks for the info. At 125K input flow would need to be limited to say 2.5-2.7 to get a consistent 70 degree rise. Very cold inlet water and or scale could make the max flow much lower to get near 125F supply. A functional mixing valve would be a must to handle the hot HX block heat burst. I hope someone didn't sell this unit as a great DHW generator. A storage tank would make it a better performer but the small combi is usually the result of economy of funds and space choices.
0 -
Very true bjohnny… ghost flow through a crossover could be a possibility. That’s an easy test for sure. It was at 140dF, I moved to 120dF and it presents same behavior.
My sales guy offered rep contact but I’ll take it anyway to confirm.
Need to check pressure HR.. we have pressure redux valves from yesteryear on all mains and they can definite fail.
kcopp is correct… no bypass valve visible that I can tell on cold inlet, just flow propeller body that sensor clips to/around.Good insights Teemok. When I saw max rate of 125k I was a bit surprised. It would perform far better with a storage tank off of these connections as the manual options. House flip, so I’d say budgetary comments are correct. I’d love to put a mixing valve on there to see if that burst can be turned into a choked heat mass than can keep up with the draw.
1 -
You need a mixing valve set to the desired temperature and most importantly a flow limiter on the hot supply output (post mixing valve if you use one). Maybe the mixing valve alone will limit hot side flow enough. Not sure about that. @hot_rod will know. Tell me your coldest incoming water temp. and I can get give a close flow rate for a desired supply. A low as possible would be best 120F is as low as I'd go.
Edit: The mixing valve alone will not do it. A ball valve set at the right flow rate measured by supply temp with the handle then removed would do it.
1 -
I measured cold inlet at 46dF the other day.
0 -
-
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements