Uponor zone control board fuse blows and relay is cycling every second

I think that I have two problems on my Uponor three zone control board (A3031003).

Problem 1: The unmounted actuator for zone one does not rotate even after being powered for more than five minutes. The board’s 4 amp fuse blows instantly when the actuator is rotated manually (the end switch is disconnected).

Problem 2: A relay on the control board is short cycling every second when a new Taco zone actuator end switch is connected. It does this when the actuator is in the open or closed position.


any ideas? Thanks

Comments

  • 109A_5
    109A_5 Member Posts: 2,004

    " The unmounted actuator for zone one " is probably defective and should be replaced.

    The " new Taco zone actuator " may not be compatible with this control module, it may draw too much current.

    What happens if the " new Taco zone actuator " is left disconnected and you just jumper R1 to R2 of that zone ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Billiambob
    Billiambob Member Posts: 9

    Thank you for your response.

    Problem 1: I already tested both actuators using a temporary plug in 24VAC transformer and both operated normally. The motors rotated and end switches connected. I will repeat this again and measure the current draws. I will also get the draws with the actuators mounted in place.


    problem 2: I will try the jumpers you suggested, thanks.

  • 109A_5
    109A_5 Member Posts: 2,004

    " Problem 1: The unmounted actuator for zone one does not rotate even after being powered for more than five minutes. The board’s 4 amp fuse blows instantly when the actuator is rotated manually (the end switch is disconnected). "

    The actual zone valve may be jammed so the actuator can't move it. I don't think it should blow a fuse when manually rotated.