1 pipe steam returns hot?

Kjmass1
Kjmass1 Member Posts: 275

Is it normal for the returns after the main vents to get warm during long cycles like we are having now with the cold in the northeast? I had re-pitched a return that had some obvious sags and low spots, I’m noticing the return pipes must be getting some steam traveling back through them?

Radiators are filling fully, no signs of pressure.

Comments

  • Paul S_3
    Paul S_3 Member Posts: 1,287

    Dry and wet returns will get warm and eventually hot. It's water that condensed from the steam. Are you having issues with the system like water hammer etc

    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Jamie Hall
    Jamie Hall Member Posts: 25,352

    If these are steam main extensions — sometimes called returns — that is to say they are directly connected to the steam mains, no traps or whatever — of course they will get steam in them. Slowly, perhaps, if there are no vents, but inevitably.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Kjmass1
    Kjmass1 Member Posts: 275

    thanks- no traps, just a step down in pipe size from the main to the smaller return extension pipe back to the boiler.

    Guess I was surprised they would get that hot even all the way back to the boiler. Worth insulating those?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,934

    @Kjmass1 I am assuming this is overhead piping. Is your vent located at the end of the main where it joins the return? Or back by the boiler?

  • Kjmass1
    Kjmass1 Member Posts: 275

    correct, ceiling of basement. Vent is located at end of 40’ steam main (a couple of big gorton vents). No venting at the boiler. The other 20’ main doesn’t have a main vent to try and slow that side down.