Been researching some as i have a customer that has been blowing pipes on a steam system. Noticed one boiler has two supply off boiler into 90s into a header, all undersized. The header turns 90 on the horizontal to drop off the equalizer into a tee. Then on the far end of the header, the steam supply to main line runs vertical up. Most of the diagrams i see have the steam supply to building between the last boiler steam supply and equalizer line. Any issues that i should be aware of? Going to recommend to client to change header to manufacturer recommendations anyways so now is the time to change it. Its the far boiler in the first picture.

Thanks

Comments

  • pecmsg
    pecmsg Member Posts: 5,571

    look at the install manual. The proper piping and sizing is in there.

    That is wrong.

  • londonrefrig
    londonrefrig Member Posts: 10

    Fair enough, just wondering on the why its wrong. For me, understanding the reason makes me a better mechanic, especially when it isnt always laid out in a manual.

  • delcrossv
    delcrossv Member Posts: 1,632

    The header's purpose is to separate any ejected water from the flow of steam. Sort of an external steam chest. The present arrangement, especially the boiler on the left, pretty much ensures a lot of water will go up the supply.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • londonrefrig
    londonrefrig Member Posts: 10

    For sure the left is a no go. Surprised it hasnt damaged the boiler through expansion. I figure all the water sucked out the boiler is keeping header expansion to a minimum. Lol

  • pecmsg
    pecmsg Member Posts: 5,571

    As I said download the manual. It’s all in there!