Near boiler piping question
Been researching some as i have a customer that has been blowing pipes on a steam system. Noticed one boiler has two supply off boiler into 90s into a header, all undersized. The header turns 90 on the horizontal to drop off the equalizer into a tee. Then on the far end of the header, the steam supply to main line runs vertical up. Most of the diagrams i see have the steam supply to building between the last boiler steam supply and equalizer line. Any issues that i should be aware of? Going to recommend to client to change header to manufacturer recommendations anyways so now is the time to change it. Its the far boiler in the first picture.
Thanks
Comments
-
look at the install manual. The proper piping and sizing is in there.
That is wrong.
0 -
Fair enough, just wondering on the why its wrong. For me, understanding the reason makes me a better mechanic, especially when it isnt always laid out in a manual.
0 -
The header's purpose is to separate any ejected water from the flow of steam. Sort of an external steam chest. The present arrangement, especially the boiler on the left, pretty much ensures a lot of water will go up the supply.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
For sure the left is a no go. Surprised it hasnt damaged the boiler through expansion. I figure all the water sucked out the boiler is keeping header expansion to a minimum. Lol
0 -
As I said download the manual. It’s all in there!
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements