We Got Steam Heat - wish I never read this book

bfinacchio
bfinacchio Member Posts: 1

It's incredibly frustrating and disheartening to try and find a contractor who adheres to even one thing mentioned in this book. None of the contractors I interviewed and one was recommended by the website, was going to insulate the near boiler pipes. They would do it for more money though. And no one even cared about the chimney. They actually said "Oh a contractor might tell you that your chimney should be lined but that's not true". One at least was willing to look at it as part of the job, since I mentioned it, the other was not.

Both said the current piping was not the best but were not going to reconfigure it until asked.

If I ever move, I'm definitely not buying another house with steam heat. Although I love the humidity and charm of it from an aesthetic perspective, it's a nightmare to find a contractor who knows or wants to do the right thing by the customer.

Mad Dog_2Long Beach Edsteamismyfriend
«1

Comments

  • Steamhead
    Steamhead Member Posts: 17,505

    Where are you located?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • pecmsg
    pecmsg Member Posts: 5,571

    steam and humidity?

    you want a contractor to insulate and not get paid?

    Where is this house?

  • Intplm.
    Intplm. Member Posts: 2,338

    @bfinacchio I sure have heard this before, and it is certainly understandable. However there are folks who continue to work with steam. On this sight you can click on the find a contractor setting and go from there.

  • ethicalpaul
    ethicalpaul Member Posts: 7,050

    was going to insulate the near boiler pipes. They would do it for more money though.

    This is reasonable. They aren't going to quote insulation as part of their base quote when they know the competition isn't going to either. Of course they are going to charge money to do more work.

    Although I love the humidity and charm of it

    Steam heat doesn't provide any different humidity than forced air, unless your system is full of leaks, which would be a Bad Thing™

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    PC7060delcrossvLRCCBJ
  • Intplm.
    Intplm. Member Posts: 2,338

    Instead try this explanation. Steam heat should not be thought of as a system that will provide humidity as a desirable source. Vents on radiators do indeed offer some humidity in operation but to say it doesn't any differently then warm air?

  • DCContrarian
    DCContrarian Member Posts: 883

    The same house with forced air will have more infiltration than with radiators. Forced air relies on creating pressure differences within the house to get air to flow, some of that pressure difference will cause infiltration from the outside, which is what causes houses to get dry in the winter.

    delcrossvmattmia2
  • delcrossv
    delcrossv Member Posts: 1,631

    +1. Absent infiltration, people exhale a good deal of humidity.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • ethicalpaul
    ethicalpaul Member Posts: 7,050

    I'd have to see real data to believe this. Pressure differences within the house is not the same as pressure differences outside the house.

    I would say that the vacuum caused by the exhaust of combustion gases greatly overrides any possible difference due to forced air blower.

    at any rate I hope we can all agree that it's misguided to think that steam heat provides better humidity

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Intplm.LRCCBJ
  • Intplm.
    Intplm. Member Posts: 2,338

    I hit the like but wanted to do the LOL.

  • ethicalpaul
    ethicalpaul Member Posts: 7,050

    You can edit your clicks

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    LRCCBJ
  • Intplm.
    Intplm. Member Posts: 2,338

    But it doesn't allow for both. It only allows for one.

  • ethicalpaul
    ethicalpaul Member Posts: 7,050
    edited January 18

    Ahh you didn't say you wanted to do both 😉

    Yeah a "friendly LOL" would be a good one in addition to the "I'm laughing at you LOL" that some people use on my posts 😅

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Intplm.
    Intplm. Member Posts: 2,338

    LOL kindly submitted .

    ethicalpaul
  • LRCCBJ
    LRCCBJ Member Posts: 750

    They laugh because they have no possible rebuttal for your careful research and documentation………..and they resort to ad-hominem attacks because "you're not a plumber". BS

    delcrossvethicalpaul
  • Intplm.
    Intplm. Member Posts: 2,338

    No.. sorry for that . My attempt at humor was not meant to mock the original post but only to poke fun at myself and to rib @ethicalpaul a bit. Sorry for the misunderstanding.

  • delcrossv
    delcrossv Member Posts: 1,631

    We need a steam heated house with ducted combustion air.

    That said, one pipe does add some minimal humidity via the vents. And considerable humidity if the vents are bad. 🤣

    I do wonder why steam heated buildings "feel" more humid though- no data, just personal experience.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    RTW
  • Intplm.
    Intplm. Member Posts: 2,338

    I very much agree. Steam heat feels so much more comfortable. I grew up as a kid with one pipe steam heat. A Sears boiler of all things. My Dad made me in charge of keeping it at the correct water level. It was a manual feed. (Was probably even a Sears house.) The comfort level was always there. I don't remember being uncomfortable in the dead of winter. Warm air, while it can be a nice system I have never been as comfortable.

    RTW
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,651

    I have installed more fiberglass insulation than I wish to remember. Do you really wanna pay a plumber or steamfitter (highly skilled trade) to install insulation? It's something the HO can do or hire a handyman for much less $$.

    If the client insists, I give them a professional insulating outfit. The anger will wear off. Atleast you know tons more going foward. Mad Dog

    JohnNYScottSecor
  • LRCCBJ
    LRCCBJ Member Posts: 750

     The comfort level was always there. I don't remember being uncomfortable in the dead of winter. Warm air, while it can be a nice system I have never been as comfortable.

    The steam system is terrific at radiated heat due to its elevated temperatures. You will always "feel warmer".

    The FHA system has no radiated heat. It does have air that flows across your skin that is typically lower than body temperature………….so, you will always "feel colder".

    I have probably the finest FHA system ever designed. Totally silent. But, I have to keep the 'stat at 70°F. A steam system would allow me to go down to 68°F. I have mitigated the FHA issue with moisture (typically down around 25%). I maintain the large room at 40-45% manually using a stovetop burner delivering steam and running constantly when occupied. Large comfort difference.

    Intplm.ethicalpaulLong Beach Eddelcrossv
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,934

    Warm air can be excellent heat ….if done properly. Although I prefer steam and HW warm air needs to be done right and is less forgiving.

    Proper airflow with not excessive velocity and careful location of supplies and ductwork that is sized properly will give you a system that is quiet and heats or cools well.

    Ducted heating or cooling has more things that can be done wrong on the install that gives it a bad name.

    Most of the USA is heated by ductwork. Steam and hot water is a lot smaller %

    My old boss was a PE. He designed a system for a big shot owner of a department store so this thing had to work.

    You couldn't even here the system rum when it was on

    delcrossvLRCCBJLong Beach EdMad Dog_2
  • pecmsg
    pecmsg Member Posts: 5,571

    with all these discussions of steam, hot water , , radiant, heat pumps whatever the common denominator when done right!

    Mad Dog_2
  • delcrossv
    delcrossv Member Posts: 1,631

    I have forced air at my house. (Originally gravity hot air). Took looking through several contractors but found a company that pulled out all the 6" round and MADE a new system on site- all rectangular duct sized for flow rate ,"pair of pants" splits ,the works. It is quiet and even.

    That said, I do have to keep a higher temp than I would have to with steam or hot water.

    Cost wise, doing this was probably comparable to installing HWH. But i was able to reuse some room risers. Outside of commercial installs, no one does FA that way anymore.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    LRCCBJLong Beach Ed
  • londonrefrig
    londonrefrig Member Posts: 10

    Biggest reason forced air is the rezzi choice here is cost. Any idiot, drunk or high, can slam together some duct, a couple runs, half **** a return or two and gas a furnace. Throw in an ac and you got yourself a humdinger of a temperature regulating system for your home. Sounds like crap, heats like crap, half the rooms are too cold, hot or noisy. But hey, the price is right. And in 10 years, you get to replace the system because the parts aren't available or too expensive vs replacement costs.

    A well thought/planned out air system can work ok, but thats not possible with the "quality" of work home builders demand. Hot water or steam is out of the question except on custom homes.

    Probably why I no longer do residential work.

    delcrossvMad Dog_2
  • DCContrarian
    DCContrarian Member Posts: 883

    I'd say the big reason for the popularity of forced air is that air conditioning is essentially free once you've installed the ductwork.

    Mad Dog_2Waherethicalpaul
  • delcrossv
    delcrossv Member Posts: 1,631
    edited January 19

    So do they put supply registers low, optimized for heat, or high, optimized for AC?

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • delcrossv
    delcrossv Member Posts: 1,631
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    guzzinerdJohnNYLong Beach Edethicalpaul
  • Jamie Hall
    Jamie Hall Member Posts: 25,351

    Given the OP's comments, @JohnNY , I'd say you dodged a bullet on that one. None of us need clients of that calibre.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    JohnNYDan Foleyguzzinerddelcrossv
  • pecmsg
    pecmsg Member Posts: 5,571

    your free to use anyone you want. This is what I recommend and advise!

    Dan Foley
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,651
    edited January 19

    "You wouldn't even know a diamond if you held it in your hand...." Steely Dan

    When the vast majority of Plumbing & Heating contractors do marginal work, at best, we that don't, have to justify ourselves to THAT Lowest Common Denominator....very frustrating, demoralizing & aggravating. Mad Dog

    Long Beach EdDan Foleyguzzinerddelcrossv
  • delcrossv
    delcrossv Member Posts: 1,631
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    DCContrarian
  • LRCCBJ
    LRCCBJ Member Posts: 750

    I have a question on how they did it? How did they get sufficient duct size through 2x4 walls? 3 1/2 x 14 1/2 is probably good for a single vent. They would have needed to open up all the walls on the first floor………….to get to the second floor…………???

    The basement probably needed 20" x 20" mains…………….???

    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,631
    edited January 20

    Yep. One riser, one vent. Mains are split at the air handler so mostly 8 x 18s

    I was doing a lot of other work, so opening walls wasn't a big deal.

    Return into the EAC is 18x24.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • LRCCBJ
    LRCCBJ Member Posts: 750

    Well done.

    That is a lot of work.

    This place has similar…………..built from scratch in 1989. Silent…………except, if you are really listening closely in the middle of the night, you can barely hear a whisper when the bedroom unit starts. The furnaces are in the basement.

    Just try to find a retrofit CAC system that comes anywhere near close to these levels.

    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,631
    edited January 20

    Yeah. Not unless it's a custom build with a lot of subsequent drywall work. 😉

    I don't see how someone can get quiet with tiny, high velocity ducts.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    LRCCBJ
  • pecmsg
    pecmsg Member Posts: 5,571

    like everything else, when done properly you’d be surprised

    Long Beach Edmattmia2
  • LRCCBJ
    LRCCBJ Member Posts: 750
    edited January 20

    @delcrossv

    I don't see how someone can get quiet with tiny, high velocity ducts.

    Like everything else, when done properly, you'd be surprised. Very cost effective too:

    delcrossv