As a combi boiler has the turndown ratio is an oversized unit as much of a concern as a ci boiler?
0
Comments
-
No — but you still want to get close…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
It becomes much more important if there is zoning involved. The more oversized it is, the greater chance that the lowest trundown ratio will be more output than the smallest zone can dissipate. The mass of a cast iron boiler can buffer somewhat. The low mass of a mod con is going to short cycle without some sort of short cycle logic on a zone that is smaller than its lowest turndown ratio.
0 -