Follow up to previous post
As a follow up to my previous post about a radiant heat system I installed, I’m realizing now that I believe I misinstalled the mixing valve gaskets. The mixing valve came with 2 gaskets with screens that have deep pockets to catch debris and one flat gasket for the mixed side. I believe I put the ovaled side of the screen pushing into the valve which is holding the check valves open and giving me hot water on the cold side of the valve. I’ve attached photos. I looked through the literature that came with the valve but it doesn’t say anything specific about the orientation of the gasket. Let me know if you guys think this would be enough to hold the check open. Thank you.
Comments
-
Could be. Worth taking apart and fixing right, anyway. The screens are domed that way to let debris slide to one side and not block the flow (too fast anyway…).
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
you really don’t need either the screens or checks in a hydronic application.
The checks are for compliance to the ASSE 1070 listing, for an “anti scald” DHW application.
Thermostatic mix valves have low cv to start with, any spec of debris in the screens will reduce the flowrates even further
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements