Airplane take off!
what is the problem when i turn the heat up —few degrees (usually first think in the morning) and some radiators sound like are taking off —spitting water out of vent. again..usually when i turn the heat up after lowering it during the night. thanks
i have a 1 pipe system
Comments
-
Need pictures of the near boiler piping from a distance.
0 -
-
see photo
s…..i have since insulated the pipes …….
0 -
Pressuretrol seems set correctly assuming the dial inside is at the lowest setting of 1. Definitiely as mentioned clean that pigtail if you haven't already. If it is dirty or blocked the pressuretrol will not sense the true pressure in the boiler allowing pressure to rise higher than settings.
Did this problem just develop recently? What do you have for a main vent and is it working?
0 -
-
kind of been an ongoing problem….main vent is hoffman 75 …..never changed it…how do you know if that is the problem or needs to be replaced?
0 -
-
here are photos of that pipe capped off….
0 -
Go in the basement and watch a cycle. When steam reaches the header and starts travelling down the main (you can feel it through the pipes, won't be able to keep your finger on it) you should be able to tell if the main vent is releasing air. You can listen, feel or use a visual such as match/candle smoke or hanging a thin strip of paper towel above the vent. If you just can't tell then take the vent off and while holding it upright blow through the bottom. Should be able to blow air through it.
Have long is your main and what size pipe?
Have you checked the boiler size vs your connected radiator EDR?
0 -
Why and how much do you turn the thermostat down each night? Steam radiant heat works best by maintaining a consistent setpoint.
0 -
Not practical for many.
0 -
example….i may put down to 68 at night….then first thing in morning….i will put to 70 or even 71 (old 3 story 100 year old house! — no insulation in walls!).
0 -
-
old thermostat….programable real basic….need to switch over!…
0 -
Doesn't anyone see a problem with this piping?
I think maybe 1-1/2". copper risers going to 2" mains might be a reason for getting wet steam into the mains, but maybe it's just me!
I can only guess at the pipe sizes from the picture but I believe this is what is going on under that insulation.
The installer followed the manufacturer's piping arrangement perfectly, but the manufacturer does not tell you how to connect to the rest of the system. You need some common sense for that. 1'1/2" copper is not the right choice in my opinion. I thins at least 2" for good measure, and I might choose iron/steel pipe and fittings over copper. But that's just me.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
Supplies shouldn't be smaller than the mains they're feeding. 😬
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
another photo…..so the problem is the copper going into the steel at the top?
0 -
Give them a break he only had 1 1/2" on the truck😊
How is the boiler water level when the boiler is steaming? Does it stay rock steady? Move up and down gently total movement under an inch? Or bounce up and down violently?
0 -
-
will look next time…..
0 -
What vents do you have on the radiators?
—
Bburd0 -
hoffman vents….
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements