One radiator doesn’t heat. Is it imbalanced venting?
there are two massive radiators on the first floor, on two separate risers. The right one heats halfway when the left one has a gorton 4 on it. It doesn’t heat at all when a no 6 is on it. The mains heat roughly at the same time but it seem all the radiators on the left riser heat super fast and all the ones on the right struggle to heat. Is it possible there’s so many radiators and vents on the left it pulls all the steam to that riser leaving nothing for the right riser?
Comments
-
the riser that isn't heating either needs more venting or has water sitting in it somewhere or possibly has more restrictive piping. what happens if you close a couple radiators on the riser that is heating? what happens if you run a long cycle?
0 -
Improper near-boiler piping can cause this- post a pic of yours.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
I use 4- D Gortons on radiators , even double venting if needed . Check radiator has a pitch to valve , old vents do go bad , if it’s your house try a Varivent , or Dole adjustable or other brand of adjustable vent . Only top venting gives less heat than a middle vent , both together give the most . Check steam feed pipes below to see if there is a sag, but you don’t mention noise or nocking , it’s probably a bad vent on radiator.
0 -
slow down the warm riser rads
known to beat dead horses0 -
I actually removed the vent on the slow radiator and it helped only a little. I also removed the main vent in the basement for that line and it didn’t help speed up the heating much either. It’s like all the pressure is going to one riser leaving nothing for the other riser. Is it possible the boiler is too small
0 -
-
0
-
-
it looks like there are 3 mains coming out of the boiler. Might that be the issue
0 -
If that is a relatively large boiler with risers on both ends, the riser to the main between the risers is incorrect. The risers to the mains have to be between the boiler risers and the equalizer. if those 3 pipes going up are 3 separate mains, those have to come off the boiler header separately, not be combined to one riser like that.
1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements