Triangle Tube Prestige - b 26 LWCO error - psi 2 - need help!
Would truly appreciate any help for a diy troubleshooting. It is 19 degrees out here in Massachusetts! Thanks, Rob
Comments
-
Is the shut off valve on the boiler fill line open? If it is and the pressure still doesn’t rise to at least 12 psi, then the fill valve may be bad or clogged.
In that scenario, find a boiler drain near the boiler on the hydronic piping, connect a washing machine hose to that and the other end to a potable connection and slowly manually fill the boiler until you have 12-15 psi on the gauge. It should operate fine if there’s no major leak on the system, but the issue of the fill valve will need to be addressed soon.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
thanks so much!
Apologies for the dumb question but where is the shut off valve on the fill line located? 🙈
0 -
I’m sorry, but I can’t see into your house from mine.
If you post more comprehensive pics from further back, I may be able to locate it.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.-1 -
haha sorry!
Maybe this helps?
0 -
0
-
The fill line valve has a blue handle and is open in the first pic way to the right. Your water feed is bad but you may have a leak as well. Look into the bottom of the boiler inside and see if the copper pipe in the middle going to the bottom has a leak or corrosion there that's where the LWCO is located and they go bad I've replaced a few kind of common on these. For now fill it with a double ended hose from anywhere with portable water to 15psi
0 -
This is the fill valve. If you raise the lever straight up, it should flow water to the boiler while it’s up, unless the valve is clogged. Close the lever once the boiler reaches 15 psi.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The pressure regulator may be plugged up lifting up the handle briefly may help.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
Is that 25 psi with the boiler hot or cold?
If it’s 25 psi cold, you need to let some water out until you get back down to 12-15 psi.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements