Rectifier fuse vs. dual element or time delay
does anyone know what a rectifier fuse is, and can a dual element or time delay be used in it’s place even if only temporary? We have a panel pictured below that controls a large number of electric baseboard heaters. The panel has rectifier fuses in them, and four are bad. The issue is that we can not find these locally and I was planning on using 20 amp 600 volt time delay fuses, until we can get the rectifier type. All heaters are 240 volt. I know I would have to install a temporary fuse block as the existing type are bolt in. Any suggestions would be much appreciated. Thanks to all.
Comments
-
I can't help you on this from experience, but to tell you that the fuses are probably protecting a circuit that has some sort of rectifier in it. Perhaps to change AC voltage to DC voltage. I would think that a standard fuse may blow prematurely if the inrush voltage spike of the circuit is excessive. A time delay may be a temporary alternative for now. I have a feeling that the standard and time delay or slow blow fuses are not designed for that application and may fail (blow) sooner that the proper fuse.
I do not think the standard fuse or the slow blow fuse will damage the equipment it is protecting. I think it will just blow before it needs to. That said, you might want to take a good fuse and put it in the failed fuse location and hope that the temporary fuse will work in the place that you swiped the fuse from. the problem circuit may have more duty cycles and will cause the regular fuses to fail, while a circuit that did not have a blown fuse may have less duty cycles therefore the non rectifier fuse may last longer there.
Just a thought,
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
-
Rectifier fuses are used in electrical systems to protect rectifiers from damage. They convert alternating current (AC) to direct current (DC) using diodes. Rectifier fuses prevent backflow of current, protecting the rectifier from reverse voltage and overcurrent conditions12345
First time I ever herd of them.
1 -
Hello zepfan,
Rectifier fuses are often found on Thyristor (SCR, TRIAC) or IGBT type motor drives and heating equipment that basically works like a light dimmer or Variable Frequency Drives to control motors and/or heat output of resistive heaters. They provide better protection to the equipment.
You probably can use another type of fuse temporally but if something bad happens it increases the chance of damage to the equipment. Why did the fuses blow in the first place ? Is there damaged equipment already ?
looks like there is plenty of KAC-20 type fuses on eBay for much better prices than from normal vendors.
Be safe, wear your PPE.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
thanks to all that responded to this. I ended up ordering the rectifier fuses off of eBay (hopefully they are good) they cost a fraction of what I was quoted locally and the lead time was less.
I went by the building today and could not find anything downstream of the fuse that was any type of an electronic device. From the the fuses they all go straight to a section of resistance heat. I don’t know why they used these specialty fuses. The only thing I can come up with is the panel is a Honeywell pre wired panel that is about 50 years old. Maybe they used those fuses to save room? Thanks to all0 -
I think fuses to protect rectifiers or other semiconductors are quite fast. If you have a rectifier system powering heating elements there shouldn't be any big surge currents because there are no capacitors to store energy. The key parameter to look for is it it^2 rating of the fuse.
john
0 -
You'd be surprised. The initial surge current into an electric heating element is very large indeed.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements