Eccentric Reducer Coupling on two pipe steam condensate returns?
I was wondering if these reducers on condensate return lines should be eccentric reducer couplings instead of regular reducer couplings. System is running ok but it seems like these condensate returns on this two pipe steam system would be holding water. Not a lot of water as the returns seem to be pitched well but some.
Comments
-
If the condensate is flowing through the strainer and then through the reducer, it's fine the way it is.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
Hello naildriver61,
Looks like it has been that way for quite some time, any issues ? I suppose muck could accumulate at the transition from the larger pipe to the smaller one. Did they reduce it just to accommodate the strainer ? Are both those pipes with strainers returns ? When was the last time they were cleaned out ?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
They both have full flow 250's. I clean them out each year and were not that debris laden. I was just wondering about the fittings as the steam runs all have eccentric reducers.
0 -
Well with steam you don't want to have (or minimize) puddled condensate in pipes that carry steam, so eccentrics help solve that issue if installed correctly. If the pipes pictures are always full of water the big issue is flow restriction by being reduced in size, may not be an issue in your case.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
There shouldn't be steam in returns to contact the pooling water and collapse and cause hammer. Standing water in returns is fine as long as it isn't blocking someplace that air needs to move.
0 -
I have had people tell me that any standing water in a supply or return will cause leaks. Not something that I totally believe.
In the above case traps and strainers are always smaller than the return lines they are connected to. If you line size traps they will always be oversized. probably the reason for the reduction. Eccentrics would be better, but they cost $$$ and not always readily available now.
Reducing 90 looking down with a close nip and a regular 90 will work as well if the return on the outlet is lowered.
1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements