Trying to troubleshoot knocking sound, likely kettling, in Utica boiler. Service Tech recommended replacing circulator pump after checking chamber, changing nozzle size and bleeding system of air.Could an old baseboard circulator pump cause kettling in a boiler ? Thanks

Comments

  • hot_rod
    hot_rod Member Posts: 23,816

    kettling or percolating sounds often indicate the boiler is scaled inside.

    If so a cleaner needs to be run for a day or so to loosen and flush.

    But a sound is in the ear of the beholder. It could bean air noise, pump noise, combustion noise, etc.

    The cleaner wouldn’t hurt regardless.

    Is there any leaks that may be causing fresh water to enter? That scales a boiler quickly.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    jringel
  • Jamie Hall
    Jamie Hall Member Posts: 25,262

    Sound is tricky — but if this sounds as though it is coming from the boiler and not the pump, it's not the pump. I'll go with @hot_rod .