Crane Boiler for water baseboard heat

I have a 1921 home with a Crane boiler system for water baseboard heat and it works perfectly. However I had it serviced last week and the young man from the local heat and air place used all my Bell & Gosset oil. I was told to just use a few drops in each reservoir a few times a year. Now I have a large spot of oil under my boiler motor. I am hopeful but worried that the excess amount of oil will damage the motor. Any thoughts. It’s wonderful heat and do not really wish to replace the unit.

Comments

  • hot_rod
    hot_rod Member Posts: 23,773

    a couple drops on both motor cups. That square cover you see with the oil cup has a cotton wick below that holds the remainder of the B&G oil tube. If it is saturated it will run out.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    techegirl71
  • Jamie Hall
    Jamie Hall Member Posts: 25,230

    If a little is good a lot must be better…. oh well. Probably won't hurt anything, though.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    EdTheHeaterMantechegirl71
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,691

    Over oiling is not a real problem but can cause a problem in the future.

    When you over oil the motor bearings, any excess oil will spill over and leak out of the oil cup and find its way on to the rubber motor mounts. over time that oil will cause the rubber to soften and cause the motor shaft and the pump shaft to move out of alignment. When that happens you will start to have coupling failure on a regular basis. If you find yourself in that situation you will need to replace both motor mount rings so the shafts line up properly. Part number 118223 from B&G or you can use this part number from Armstrong to get less expensive motor mount rings 810120-000

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    bburdtechegirl71
  • techegirl71
    techegirl71 Member Posts: 3

    you are great. I appreciate your quick responses. I am going to relay all this info to he young man coming back tomorrow to look at what he’s done.

  • techegirl71
    techegirl71 Member Posts: 3

    I also found an owners manual pdf online from 1952 that I believe will be a good resource.

    just added a photo I forgot to add earlier.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,807

    Nothing in that picture is 1952 although the pump may be the same as the older pumps. The boiler looks like70s-80s

    techegirl71delcrossv
  • delcrossv
    delcrossv Member Posts: 1,524

    Agreed

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.