Is there a CI gas boiler that is power vented?

Cyclist77
Cyclist77 Member Posts: 68

Thought I would tap the knowledge base here because as I search different manufacturers the info says power vet but as get into the manual it seems they are actually direct vent.

So is this type of venting not available on a CI gas boiler?

Comments

  • Intplm.
    Intplm. Member Posts: 2,342

    Almost any boiler (almost) can be power vented. It's not so much the boiler as it is more to the reason to use a power venting system.

    Do you have a viable chimney. If so, use it.

  • Cyclist77
    Cyclist77 Member Posts: 68

    I do have a clay tile lined chimney but it is my understanding that it would need a SS liner.

  • hot_rod
    hot_rod Member Posts: 24,070

    it will be a bit noisier if that matters?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • pedmec
    pedmec Member Posts: 1,148

    Steam or hot water? Burnham makes steam and hot water that is power vented. Any models that will be labelled with PV in there model # are power vented. But keep in mind that although its power vented you still might have to make provisions for combustion air, This is why most boilers, water heaters and etc are direct vented. It's easier to just run just the piping for the combustion than to add another appliance (power vent kit) that can fail.

  • GroundUp
    GroundUp Member Posts: 2,242

    Weil McLain, Burnham, Crown, Peerless, and several others make them. Direct vent and power vent are the same thing when referring to a cast iron boiler.

  • pedmec
    pedmec Member Posts: 1,148

    @GroundUp that is incorrect. a direct vented appliance takes air direct from outside and into the boiler. power vent appliance only refers to exhaust. it has nothing to do with cast iron.

    A Burnham IN5PVNI is a cast iron power vented boiler.

    A Burnham X-PV3N is a cast iron power vented boiler that can be converted to a direct vented boiler with the direct vent kit.

    Direct vent combustion appliances include 

    furnaces, boilers, and water heaters that utilize natural gas or propane that are equipped with a pipe to bring combustion air directly from outside to the combustion chamber

    .

    GroundUp
  • GroundUp
    GroundUp Member Posts: 2,242
    edited January 4

    They are literally the exact same thing on a CI boiler, whether you like it or not. Any direct vent boiler can draw room air (aka power vent) if there is adequate supply. A WM CGi for example is listed as a direct vent unit, but it is 100% a power vented boiler by definition.

  • hot_rod
    hot_rod Member Posts: 24,070

    The direct vent kit allows for exhaust and intake air in one pipe, one penetration through the wall.

    With a power vent, or an add on venter, you would need a source of combustion air into the room.

    Same with direct vent water heaters, compared to power vented models

    .

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GW
    GW Member Posts: 4,899

    here’s one I re piped for someone Friday, cast iron high efficiency. Weil McClain.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    PC7060
  • pedmec
    pedmec Member Posts: 1,148

    Taking room air for an appliance list as a direct vented appliance changes the category of the appliance to a power vented appliance and changes the clearances between windows, doors, etc. Now you need clearances of 4' And not only that you need to now make sure your following code for combustion air in the basement. Your basement needs to be big enough to support combustion or you have to bring combustion air with dampers, fan in a can, or something similar.

    PC7060
  • JohnNY
    JohnNY Member Posts: 3,308
    edited January 5

    For steam, only Burnham.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Long Beach EdIntplm.
  • GroundUp
    GroundUp Member Posts: 2,242

    So what am I wrong about? It's literally the exact same appliance, as I stated in the beginning and you argued with.