Burnham ODR - anomalous behavior after install

EricPeterson
EricPeterson Member Posts: 220

I installed the Burnham ODR on my ES2 boiler today and observed a couple of anomalies:

  1. After running for some time, I noticed that with a call for heat, the circulator was still running but the boiler was reporting that it was in Standby (Status 1) instead of Running (Status 8). As I watched, the boiler then fired up again going through the intermediate states (Waiting For Damper To Open, Spark, Flame Proving) before ending up in Status 8 where it should have been.
    I've never seen this behavior before installing the ODR.
  2. With the Boost set to 30, I observed the Setpoint go from the initial value of 153 to 163 after 30 minutes. After another 30 minutes it then went to 170.
    I would have expected it to go to 173. (the High Boiler Water Temperature is set to 180).

Any thoughts?
Eric Peterson

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,262

    The ODR is controlling the boiler circulating water temperature — as it should — maximize efficiency and minimize cycling. If it's not delivering enough heat, you may need to adjust the settings for the ODR curve.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Hot_water_fan
    Hot_water_fan Member Posts: 2,079
    1. Sounds like pre-purge. That’s a setting, maybe you never noticed it before?
    2. Likewise. Maybe it’s saying 7 then the last step is 10F?

  • EricPeterson
    EricPeterson Member Posts: 220

    @Jamie Hall - yes it seems to be doing the job. I was just expecting it to increase to 173, then I suppose to 180 if it ran another 30 minutes.

    @Hot_water_fan - pre-purge is a setting that's not available on my boiler.
    Available settings (Adjustment Mode Options):

    • HL_ (170 F) Adjust High Limit Setting
    • dF_ (15 F) Adjust Limit Differential
    • rSt (OFF) Reset Lockout
    • F-C (F) Select degrees F or C mode

    The ES2 IO Manual does document this condition (see below). I did confirm that when this condition is occurring, the boiler temperature is above the setpoint established by the ODR. Once it drops 15 degrees below the setpoint the boiler fires and transitions to status=8 (Running).
    The second condition does not apply to my setup as Start Temperature and Circulator Pre-purge parameters are not present.

    It just seems odd to me that with StA 1 (Standby) sometimes the circulator is on and sometimes it is off.
    Maybe they should have had an additional status to distinguish these two situations.

    —Eric


  • Hot_water_fan
    Hot_water_fan Member Posts: 2,079

    Pre-purge isn’t available but is listed in the manual?

  • EricPeterson
    EricPeterson Member Posts: 220
    edited January 5

    The manual is here: link

    Video of Adjustment Mode Options: