Steam Coil on Ptac

Paul S_3
Paul S_3 Member Posts: 1,288

Hey guys happy new year. We have a customer in a 100 unit apartment building with these ptac units. They have a lot of water hammer. We know that there's probably steam in the return line from a bunch of failed traps. My question is with a zone valve and a trap on the return is a vacuum breaker required?

ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,624

    Yes. On the inlet.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Paul S_3
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,230

    anwhere between the zone valve and the trap on the supply or return.

    Paul S_3