My house was built 6 years ago. I had a bad water leak that was located by a detection company by the water meter. I dug it up. The leak was between the 1" pex and the brass (?) pex adapter that is screwed into the water meter assembly. When I took the pex off, I found the adapter had severe corrosion on the pex side, and even a pinhole that went all the way through.

I replaced the fitting and got things working with no leaks, but before I bury it again, I'd like to figure out what went wrong. I don't want to dig it up again in 6 years.

I assume that brass shouldn't corrode in such a short time. Could it be the builder used a cheap fitting that was made with the wrong metals? What could cause this?

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,534
    edited December 22

    What is in the surrounding soil? Mad Dog

  • Glorious1
    Glorious1 Member Posts: 5

    @Mad Dog_2 , I don't know, it just looks like mostly clay with a lot of rocks in it. None of the other meter assembly components seem corroded. Here's a photo of the repair in progress that shows the soil.

  • psb75
    psb75 Member Posts: 912

    Use a Uponor Propex stainless steel expansion fitting from Supplyhouse. There is something in the soil or water chemistry that is degrading the brass pex crimp fitting.

    bjohnhyGlorious1
  • Kaos
    Kaos Member Posts: 257

    This. Replace all fittings with stainless.

    Also watch those crimp rings. Some are plated steel and will disintegrate in soil over time. You want copper or stainless rings.

    Glorious1
  • ChrisJ
    ChrisJ Member Posts: 16,319

    The fact that it's only eroded in one spot makes me think it was leaking. If something about the water did it wouldn't it be all around wherever it was in contact with the water?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Glorious1mattmia2GGross
  • bjohnhy
    bjohnhy Member Posts: 32

    I would also wrap it so it's not in direct contact with soil.

    Glorious1
  • hot_rod
    hot_rod Member Posts: 23,495
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    delcrossv
  • Glorious1
    Glorious1 Member Posts: 5

    Thanks for all the replies. I'm guessing it is dezincification. I assume all the other fittings on the water meter assembly (like the one the adapter is screwed into) are also brass, but no problems there. Maybe @ChrisJ is on to something, it may be related to a leak. All the corrosion is connected, and where the insert/barb portion meets the part that you wrench onto, it goes up that 90 degrees. Maybe they got some dirt between the pex and insert and that somehow started it.

    Anyway, I found a stainless steel crimp adapter and ordered that. I will have to redo the whole repair when it arrives (sigh), but I don't ever want to dig it up again. The crimp rings are copper.

  • ChrisJ
    ChrisJ Member Posts: 16,319

    Yeah...

    Though there's a hole where the leak started so maybe I've got no point.

    I didn't notice that before.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ScottSecor
    ScottSecor Member Posts: 908
    edited 12:29AM

    @Glorious1, I doubt the plumber or the builder would "cheap out" on a buried water line. I suspect this would not be the place they would try to cut corners. Most likely, what they used what was readily available at the local supplier.

  • hot_rod
    hot_rod Member Posts: 23,495

    Pretty much all plumbing brass is DZR, dezincification resistant brass now, and also LF lead free or LL low lead

    sometimes it is even stamped into the piece.

    Maybe it was old inventory or an import that wasn’t certified DZR

    Assuming the failure was dezincification, it looks like that was the cause.

    The metals in contact are all similar, so electrolysis is probably out.
    Could be aggressive soil, moisture would increase the attack

    I would tape seal the copper crimp rings

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 11,021

    looks like it was leaking when it was installed and eroded. i can't see the inside very well but is it in good condition?

  • mattmia2
    mattmia2 Member Posts: 11,021
    edited 2:48AM

    i'd use ep fittings and expansion rings if those are permitted underground which i think they are.

    i think the first ring of the barb wasn't sealed at all so water was flowing around that freely then the clamp channeled it where the groove and pinhole are and it eroded over time. stainless can be as bad or worse than brass with certain water chemistries especially those high in chlorides.

    bjohnhy
  • hot_rod
    hot_rod Member Posts: 23,495

    the meter yoke is copper and brass, i would use a brass adapter

    The farther apart the metals are on the galvanic series, the more potential for electrolysis corrosion, especially in moist conditions

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Glorious1
    Glorious1 Member Posts: 5

    @hot_rod, what kind of tape would you suggest to wrap the rings? I thought stainless would be safer, so ordered it. I hadn't considered the electrolysis issue. Maybe I should leave the new brass fitting, and wrap it in plastic wrap.

    @mattmia2, yes, the inside of the old adapter is in good condition. It is coated with a thin layer of fine, off-white material that can be rubbed off. But there is no corrosion other than the one pinhole.

  • Intplm.
    Intplm. Member Posts: 2,217

    You can also use a plastic adapter to prevent this type of deterioration. Stainless is fine but not as readily available.

    @Glorious1 you can use rubber tape found in the electrical section of your hardware store.

  • ChrisJ
    ChrisJ Member Posts: 16,319

    Technically stainless steel and copper / bronze is bad together.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • hot_rod
    hot_rod Member Posts: 23,495

    I think Uponor had a shrink wrap sleeve they wanted you to use when you spliced a pex connection in a concrete pour.

    I think shrink wrap with waterproof seal like you use on wire connections would be adequate.

    I saw a video where they poured a liquid over the shrink wrap on a wire splice. Maybe some silicone liquid??

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hot_rod
    hot_rod Member Posts: 23,495

    If you have pex "A" I would use expansion fittings. The repair coupling and adapter will cost you some pressure drop with the insert/ crimp ring type fittings.

    Shrink seal that coupling also.

    One of the brand names is where I would get the fittings. The inexpensive import brass is questionable, even with a known brand name on it.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry Weingarten
  • mattmia2
    mattmia2 Member Posts: 11,021

    I used a piece of collapsible discharge hose to isolate the gas riser in the concrete footing supporting the pedestal for my grill.

  • pecmsg
    pecmsg Member Posts: 5,328

    nothing wrong with Heat Shrunk tubing wi seal the connection

  • mattmia2
    mattmia2 Member Posts: 11,021

    other than that heat shrink in that size can cost anywhere from a dollar to $500 depending on where you buy it from.

  • Glorious1
    Glorious1 Member Posts: 5

    Well, thanks guys, but I'm going with silicone tape, which is recommended for underground fittings. It stretches so you can put it on tight, then it fuses to itself in a few minutes. Hopefully it will make a water-tight seal and prevent any soil contact. Also I rinsed all the soil off the areas I will tape, dried with paper towels, now air-drying.