6yo NTI TFT 154 Gas/Hot Water Boiler throwing error codes (Chicago area)
Starting this morning I noticed that the heat was down a few degrees and checked on the boiler.
On the Control Snapshot screen it displayed:
Lockout 109: Ignition failure occurred
Alert 448: Flame too low
Alert 293: Abnormal recycle, Flame was lost early in run
Alert 291: Abnormal recycle, Flame was not on at end of ignition period
Alert 449: Modulation rate was limited due to flame strength
I originally thought this was due to a dirty flame sensor so I cleaned it with steel wool and it fired up normally. I also cleaned the condensate drain for good measure. When I returned home this evening the lockout 109 and alerts 291/449 were present.
I cleared the lockout and alerts and it's been working fine for the last 4 hours, but it's clear I need to do some more work.
I'd love to get some input with this situation on likely causes. Hoping it's as simple as a faulty flame rod and I can have it delivered by Tuesday.
(alert 448/449 refers to lockout 138 but that lockout never triggered)
Comments
-
Hello FIshermanPete,
I'd say much more to check.
https://ntiboilers.com/wp-content/uploads/2018/12/TFT-Series-IO-Manual-2018-09.pdf
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
How old is your igniter? Also, when you cleaned out your condensate did you make sure the line that it connects to was also clean. I just had one like that, a little baffling, I pulled condensate off and after pulling the lid off the top of the HX I started pouring vinegar into the HX and it wasn't coming out the bottom. Shoved a screwdriver up there and sploosh it call came out!
Just a thought. Could be gas pressure. Lots of things to check!
Tom
Montpelier Vt0 -
Agree the list is long for things to check with lockout 109, it seemed the combination with the different alerts might narrow it down to a 'most probable' issue.
The igniter is original. I haven't yet disassembled/cleaned the HX to ensure flow. I focused on the condensate trap to make sure the float/ball was not stuck, was pretty caked with sediment on inspection but is now clean.
I've subsequently tested the venting, gas valve, and spark generator and found no issues. I do not have access to a manometer to test the gas pressure. I'm willing to buy one if that is a high likely suspect based on the errors.
Would it be prudent to go ahead and buy a new flame sensor and igniter (as both are original) and install them first before disassembling and cleaning the heat exchanger? I'd prefer to put that task off until spring.
0 -
You can build a manometer.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements