Steam boiler intake water filtering

leaking
leaking Member Posts: 111

I am in Chicago . Semi hard water , no water softener necessary. A 10 yr old Weil McLain 650,000 btu (or so) steam boiler . I read in the literature that no treatment was recommended to use inside the boiler but what about the fresh water makeup , the fill ? I have Takagi tankless for HW , and they have a scale reducing filter I use. They last 1.5 years in a 12 unit . Would using a scale reducing filter help ? Would it damage the boiler ? I believe it alkalines the water . I try to flush down the brown water every day to every week, yearly flushes I don’t remove much mud . I just don’t want to damage the LGB 6/23. But want to do what is best. Thanks all .

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,044

    You really want to maintain steam leakage. If no water is lost , then you don't have to add water .. You can start with good vents ..

    There was an error rendering this rich post.

  • Jamie Hall
    Jamie Hall Member Posts: 24,984

    You flush down the brown water every day? Or at least every week? Oh dear. I hope not. If a steam heating system isn't leaking — and it shouldn't — a boiler flush once a year is more than ample, although if there is a float type low water cutoff it should be blown down a few times a month — but that only involves a gallon or less of water.

    You're killing your boiler with that fresh water from the flushing… stop it!

    As to water treatment, some folks suggest adding a buffer to bring the pH around 10. Some folks suggest not bothering with that (including Weil-McClain). In any event, if you have no leaks, the small amount of water added is not a problem, even with very hard water.

    If you have to add more than a gallon or so of water a month — besides the LWCO water — find the leaks and fix them.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,437

    I'm in Chicago as well. I see no need for a DI filter for City water.

    8 way at 1/4 the dose on the bottle is helpful.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.