Resistance and Ohms
I’ve been told a bunch of different answers I want to completely understand. Checking resistance on motors whether single phase or 3 phase this happens to be single phase. I went across both leads GOT OL.( is it bad is it good) my mind says that’s bad. Went each lead to ground one lead read OL. The other read 17-20 MegaOhms to me motor is bad to my knowledge. What is short to ground? What is considered bad windings? Is OL ever ok? What do I look for when testing resistance on motors?
Comments
-
OL on most meters (read it as "open leads") means simply that the resistance is greater than the maximum reading possible on the meter — which is usually a completely open circuit. Which is fine, if that's what you want. 17 to 20 megohms to ground is alright.
To go back to a reading of "OL" across the leads to the motor (presumably the hot and neutral to a single phase motor). This is NOT good. The actual winding resistance, lead to lead, depends very much on the motor in question — a small motor may have 20 to 30 ohms winding resistance, but a big one may have only a fraction of an ohm. Resistance to ground should always be at least 10 megohms, and OL is better.
There is a definite "gotcha" on the "OL" reading, however: it may be that you have poor contact (or none!) on one test probe or the other. Make sure you have a very good connection and, if possible, test it.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 101 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements