Steam Valve Leak

VCard
VCard Member Posts: 15

Looking for some advice. The radiator in the images leaks from the steam valve air vent. Not sure of the exact terminology, but the hole where the air escapes. It seems that the mechanism which should close the hole during heating is failing. If the thermostat in the house is on the same temp, all day, its not a problem. But if I push the temp a couple of degrees after being out, I get about a pint of water in about an hour of running the boiler. Is this a get a new valve issue or something more. I am reluctant to DYI this because I do not see the shut off valve for the radiator. It must be underneath the floor which I cannot access, because the ceiling below (in the garage) is finished. Thanks

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,814
    edited December 13

    Yes it's as easy as replacing that steam vent, but as you know any time you touch something, the unexpected can happen. The first time I tried to clean my pigtail, the whole fitting it was screwed into crumbled in my hand.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,588

    Just shut the boiler off to change the vent.

    But there could be a lot of other things at play here:

    Radiation should be pitched towards the supply pipe

    Boiler pressure may be too high

    Piping to radiation may not be pitched…it should be higher at radiation and lower at the supply end.

    You may want to put a vent on with a slower venting rate to combat the leak. If the rad fills with steam slower, it will not be hit with a large amount of condensate all at once.

    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,437

    Try a Maid o mist or Gorton #4 on that.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.