trying to slow radiator heating, smaller vents didn't help.

Hello - I've been trying for some time to balance the heat on 9 unit 2 story apartment building. 2 years ago I hung yolink temperature sensors in each unit so, using my phone app, I can see what the temperature actually is at any give time. There is a pretty wide variation between apartments so I decided to try to adjust one apartment as a trial. I swapped out the dole vents on the 2 main radiators for groton #4s. It's been over night and it doesn't look like the temperature is dropping which makes me think the rads heating rate hasn't been affected.

The 2 radiators are about 50" long, 14" high, 12"wide. Most of the smaller rads on the system are one pipe. These bigger ones look like 2 pipe with the supply valve controlled entering the top of the rad and the return pipe in copper exiting the other side. The condensate is a wet return. So, anyone have thoughts on how to slow the heating of those 2 rads? Thanks

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 25,209

    If they are truly two pipe, with a return low on one end, then you can partially — or completely — close the supply valve and do no harm. Are these vented at the radiator, or is there a vent somewhere on the return?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Todd_33
    Todd_33 Member Posts: 69
  • Todd_33
    Todd_33 Member Posts: 69

    I'm not expert but I think it's a 1,2 combo system, the condensate goes to a wet return I think. I just posted some pics.. I'm aware that closing the valve would help, but I'm not sure tenants would consistently do that. I was looking for a way to tamp down the heat. I suggested the tenants put blankets on the rads but that met with limited success.

  • LRCCBJ
    LRCCBJ Member Posts: 672

     I suggested the tenants put blankets on the rads but that met with limited success.

    That is an excellent suggestion. I am curious if it met with limited success due to the failure of the tenant to do anything that requires a slight bit of effort?

    You do not need the tenant to consistently do anything. As you probably know, this is impossible. You set the valve yourself and monitor the temp in the space. If it is still too warm…………you close it a bit more………….repeat as necessary to get the room temperature under control. It is an iterative process and YOU are the one who must do it.

  • Todd_33
    Todd_33 Member Posts: 69

    Thanks LRCCBJ - I seem to recall that with the condensate pipe system I can partially open and close the valve to choke off the steam somewhat. I guess that's the way I'll go. Thanks - I was disappointed that the smaller vents didn't help.. I'll push the blanket solution too..

  • JohnNY
    JohnNY Member Posts: 3,302

    I'm suspicious of that union on the return. Someone put that there in an effort to deviate from what was original. My guess is there was a trap there and no air vent. Is that radiator heating from the return side as well as the supply?
    If I'm wrong then leave it and consider installing a small orifice plate in the supply valve's union.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    delcrossv
  • Todd_33
    Todd_33 Member Posts: 69

    Thanks for the input.. I'm wondering if this originally was one pipe like the rest of the rads but was converted to 2 pipe.. creating problems. There are other indications of that...