Which Navien Boiler size for Radiant only system?
Hi! I need to replace my current 12 year old triangle tube Challenger (CC125). I use radiant heat through the floors as my only heat source and have a separate domestic hot water heater. I'm located in Baltimore, MD.
I have been quoted Navien NHB 110 and 150.
My house is 4470 sq feet of radiant heated space (through the floors) with closed cell spray foam insulation. It has 4 zones- I use 2 of them. I only use 2680 Sq feet of the radiant heat (2 floors— I leave the basement and attic off). I can't imagine ever using the basement (nice and toasty as is) but turning on the attic would be 3130 sq feet.
Are either of these overkill? I was reading about an early grave by short cycling and just want to make the right decision since I'm replacing it. Thanks for any help- I have no one else to ask ha!
Comments
-
-
What is up w/ the Challenger?
0 -
-
Oversizing is of lesser consequence with modulating equipment so either would probably be fine, but it'd be up to a heat loss calculation to determine. On a side note, I too would find a different contractor that doesn't install Navien- I have replaced 17 of them this year alone and the oldest was only 4 years old. One was only 2 months old and had a leaking heat exchanger already.
1 -
All Steamed Up must have a backlog- I've called a couple times. Frank has been universally recommended across all forums. Tough timing here to need a replacement!
Re: the challenger— it's 12 years old, never had maintenance on it until 2 years ago (purchased the home) and needs a new control board. It has been going in and out of heating since early October. Since Oct. I have replaced the igniter, gaskets and flame sensor and am still losing heat every couple of days. I wish I would have just called All Steamed Up in October!! thanks for all of your advice, it helps a lot. Got a new Bosch quote instead of Navien.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements