Independence IN-4 boiler, water disappearing

Last night I noticed the water was low and added about 5-1/2 quarts.

The boiler has never been a water hog

Tonight upon checking the water level is again lower than expected

I examined the following:

Floor around the boiler

Floor under the pipe runs

The flue by looking in the damper

The underside of the automatic damper

The burner bay

No signs of water anywhere and no signs of steam in the burner bay or flue.

Any idea where else it could be leaking?

Comments

  • Steamhead
    Steamhead Member Posts: 17,380

    Probably leaking from one or more cast-iron sections above the waterline, and the steam is going up the chimney. You could raise the water level well above the top of the sight glass and see if water comes down into the firebox where the burners are. If it does, you need a new boiler.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaul
  • 109A_5
    109A_5 Member Posts: 1,670

    Also when the boiler is running look at the top of the chimney, is there a lot more water vapor than normal ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System