New Main Vent Not Making a Sound... Is It Faulty?

I recently fixed (I hope so anyway) a major failure in my heating system. I had to replace two main vents in the basement. One of the main vents does not seem to be making any sounds. No clicks. I stood under the vent during the entire heating cycle and didn't hear a thing. To be fair, it's not too far from the boiler and things are pretty noisy. Is the thing broken? The other main vent is across the room. It makes a very loud clank. It hisses like crazy a few minutes after the boiler stops running. I never paid much attention to the sound of the main vents because they're in the basement. Is this normal?

Comments

  • Steamhead
    Steamhead Member Posts: 17,380

    Shut off the boiler, remove the vent, hold it upright and blow through it. You'll know if it's passing air or not.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • pedmec
    pedmec Member Posts: 1,066

    or you can put your hand on the main at the vent location and see if the steam has arrived at the vent

  • ethicalpaul
    ethicalpaul Member Posts: 6,666

    What is the vent? Several main vents don't make noise.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Long Beach Ed
  • 109A_5
    109A_5 Member Posts: 1,670

    Hello HotChocolate1947,

    After the boiler stops a vacuum is formed an if the vent starts to cool and open the hissing noise may be the air entering the system through the vent.

    Also you could switch them to see if the behavior is the same.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • HotChocolate1947
    HotChocolate1947 Member Posts: 23

    @pedmec You mean I should try to feel for warm air from the vent. It does seem easier than taking it down.

    @109A_5 I don't think I should swap them. They are different sizes.

  • CoachBoilermaker
    CoachBoilermaker Member Posts: 347

    If the vent was stuck closed, steam would not reach it. So if the nipple and/or body of vent gets hot, you know it is not stuck closed. If it is silent, then good, you know it's not stuck open, and spewing steam.

  • 109A_5
    109A_5 Member Posts: 1,670

    Since they are different sizes the swap would be temporary, however the swap would see it the behavior follows the vent or the main.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • pedmec
    pedmec Member Posts: 1,066

    If it ain't letting air out, you ain't getting steam in.