New Main Vent Not Making a Sound... Is It Faulty?
I recently fixed (I hope so anyway) a major failure in my heating system. I had to replace two main vents in the basement. One of the main vents does not seem to be making any sounds. No clicks. I stood under the vent during the entire heating cycle and didn't hear a thing. To be fair, it's not too far from the boiler and things are pretty noisy. Is the thing broken? The other main vent is across the room. It makes a very loud clank. It hisses like crazy a few minutes after the boiler stops running. I never paid much attention to the sound of the main vents because they're in the basement. Is this normal?
Comments
-
Shut off the boiler, remove the vent, hold it upright and blow through it. You'll know if it's passing air or not.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
or you can put your hand on the main at the vent location and see if the steam has arrived at the vent
0 -
What is the vent? Several main vents don't make noise.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Hello HotChocolate1947,
After the boiler stops a vacuum is formed an if the vent starts to cool and open the hissing noise may be the air entering the system through the vent.
Also you could switch them to see if the behavior is the same.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
If the vent was stuck closed, steam would not reach it. So if the nipple and/or body of vent gets hot, you know it is not stuck closed. If it is silent, then good, you know it's not stuck open, and spewing steam.
0 -
Since they are different sizes the swap would be temporary, however the swap would see it the behavior follows the vent or the main.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
If it ain't letting air out, you ain't getting steam in.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements