Automatic Feed Valve Makeup Demand
Wcurtis
Wcurtis Member Posts: 132
edited October 2024 in Strictly Steam
when an automatic feed valve is installed does the signal to feed due to a low water level take into account a steaming condition, then wait until the returning condensate arrives and fill sightglass to a desired level?
Concerned about a possible overfill scenario and possible flooding if I'm not there to catch it should the automation fail, leakby or not take the steaming action into account.
    EdTheHeaterMan Member Posts: 12,506
    Depends on which one and how it is installed.
    Residential or commercial?
  • Wcurtis
    my apologies, residential
    Do you have a float type LWCO or an electronic LWCO?
  • Wcurtis
    edited October 2024
    float type, I do not have an automatic feeder but I had a contractor oit today looking at another job and he stated if he got the contract for a new boiler replacement he insists on this…which I currently do not have
  • Wcurtis
    Just wondering how they are rypically setup
    This model have all the features you need.
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Hydrolevel-45-122-Install-Instructions.pdf
    there is a water meter to indicate how much water is being added. There are time delay adjustments to keep the feeder from adding water so the returning condensate may be able to return and raise the water level, reducing the possibility of flooding the boiler.
    It can connect to both mechanical float and electronic probe type LWCO controls
  • Wcurtis
    edited October 2024
    sounds simple enough, I just dont trust automation like I should and I like the older stuff
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,622
    What do you mean the contractor insist? You are paying him and you get to decide. Automatic feeders are not a good idea, unless you are away for extended periods of time during the winter or you are physically or otherwise unable to check the boiler on a somewhat regular basis.
    BobC
  • STEAM DOCTOR
    And once we have you on this site, kindly utilize our services in helping you vet the contractor. It don't cost you a penny
  • STEAM DOCTOR
    And agree with Ed. Only water feeder I ever put in. When the customer insist on having one. Has programmable delay in feeding and programmable feeding amount (in theory).
  • Wcurtis
    this all started when looking for a new boiler replacement, 3rd contractor, the owner of the company came out becuase he doesnt have anyone who has been around long to understand steam
  • Wcurtis
    I am not at the house everytime the boiler operates but check it constantly when I am there, been doin it successfully for 4-years without a hitch HOWEVER if I am not around and my wife has to do things, this MAY be an option
    Jamie Hall Member Posts: 27,582
    I am not averse to automatic water feeders. I also have a VXT on Cedric (my big boiler). All kinds of nice features. And, with a float type low water cutout, pretty reliable (if I remember to blow down the LWCO…).
    They are not a substitute for checking the boiler regularly. If nothing else, the one I have has a meter on it telling me if it thinks it needed to add water — useful to know.
    They can overfeed. This is true. but it's not common at all. Set correctly they won't overfeed under any reasonable operating condition, however.