Adding zone to forced hot water heat system
Hello I'm trying to split up my baseboard heating into two separate zones. I traced all of my piping and this is what I have going on. (See included pictures of pipe layout and unit) My plan is to have the living room/kitchen on a zone, and the bed rooms on another. This isn't really in my wheelhouse as I am an electrician by trade. From what I figure, if I add a zone valve to the returns, I can control water flow in either side of the house independently. For example, if I close the return valve on what I labeled "r2" then the water will not complete a circuit through the supply because the return is blocked. Therefore the living room/kitchen heaters will not heat up.
I tested this theory by closing one of the two ball valves on the existing returns. Seems to work. Is this the best way to go about this? I know nothing about the mechanics of how these type of systems work and don't want to introduce any issues. I’m sure it’s probably more nuanced than I’m aware of but that’s why I’m asking you guys. Thanks!
Comments
-
That will work. You are fortunate that you can split it that way so easily!
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Install a separate 120/24 volt transformer with a capacity of 40va
Install a zone valve and a thermostat for each zone. Make sure each new zone valve has a built in isolated end switch
Wire from the new transformer to the thermostats and zone valves. Use the new transformer to operate the new stats and the zone valve power.
Connect the two end switches from the zone valves in parallel and wire it to the terminals where your present thermostat is wired to. Remove and abandon the old thermostat wire.
0 -
Here is the best way to do this. Have a valve near the zone valve inlet location, and then have a valve at the outlet location. That way if you need to service the valve that requires opening up and letting the water out, you do not need to drain the whole system. And you only need to add 2 valves since the existing valves were installed with very short copper pipe between the fittings. And since those crimp fittings are a one and done i would suggest that you add longer pipe stubs to those crimp fittings for future use in the event you need to cut some off in the future, You don't need to throw those new valves away.
Or you can add the valves on the PEX side, with valves above and below.
I would not install the zone valves with PEX on either side, but that is a personal choice for me. No rule against it.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
And just for 💩 and Giggles I am attaching the wiring logic for your particular set up.
The SR501 on the right of the diagram is your existing SR501. Remove the thermostat from R & W at the top and connect that thermostat to the appropriate zone valve. Then run a second thermostat to the other zone valve. Then use the end switch leads (in parallel) from both zone valves to connect to R & W on the SR501. Although with your background, I'm sure you would figure it out.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
thank you for the detailed response and awesome diagrams . Very helpful. The wiring makes perfect sense to me. I’m guessing I’m gonna have to probably redo that whole section of copper where the two returns hook up because there really isn’t enough usable copper to get something on there to extend the stubs. Looks like it would be easier to cut the 3/4 pipe below and then solder on a tee and then go from there.
0 -
@atibbs96 Said: "I’m guessing I’m gonna have to probably redo that whole section of copper where the two returns hook up because there really isn’t enough usable copper to get something on there to extend the stubs. Looks like it would be easier to cut the 3/4 pipe below and then solder on a tee and then go from there."
That is one way to do it. You can also just stub some copper into the zone valves with PEX adaptors on either side. then use pipe hangers to fasten the copper to the board to make them stable.
Picture to follow:
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.1K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 62 Pipe Deterioration
- 907 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.7K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements