Plumber advises to keep air inlet when removing house trap
Comments
-
The fresh air vent on a house trap satisfies the plumbing code that every trap must have a vent. With removal of the house trap the home plumbing will be vented through the stack vent through the roof and possibly other fixture vents going thru the roof as well.
House traps are no longer required in most areas.
0 -
What is wrong with extra vents? I like inverted U s to prevent stuff falling into drain line.
0 -
-
When it comes right down to it, if you leave the vent installed it will be an extra vent. There's no harm in leaving it there.
0 -
I’d have to disagree. You now how the entire street (and more) venting out of the side of your house. It’s no longer a fresh air INLET, it’s just allowing sewer gases to expel at an unacceptable height off the ground. With the house trap installed, the fresh air INLET is in front of the trap, not behind it.
1 -
@Danny Scully Very good point! One would think it would be against plumbing code to leave the air inlet in if there's no trap. One wonders how often plumbers find such a setup.
0 -
Good point Grasshopper, but it's no worse than a street manhole cover. I'm keep my house trap and my Fresh Air Inlet.....Mad Dog
1 -
Real stench comes when house trap leaks and there's no vent.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements