Burnham ES2 boiler

wintermj
wintermj Member Posts: 1

My boiler worked fine last year.

This year it comes on for 1 to 3 minutes and then it shuts off.

The control panel reads STA1

There are 2 zones

One in the basement and one on the first floor.

Also, the pipes don't get hot , however the exhaust pipe does

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518

    Call Burnham tech support this morning. Mad Dog

  • Ironman
    Ironman Member Posts: 7,548
    edited October 25

    Sounds like you’re not getting flow through the boiler. It could be air binding or a bad circulator.

    What’s the pressure on the boiler gauge?

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.