Oil fired boiler replacement

caw
caw Member Posts: 1

We have an old 4 section Weil McLain boiler. There are three zones, each with a wax valve. Each zone valve can start the pump. The boiler cycles to maintain a minimum return water temperature. We would like to replace the boiler, but would prefer to fire the boiler (and pump) only upon a call for heat in one of the zones. Any recommendations for a simple way to do this? Thanks!

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,230

    Why do you want to replace the boiler? Is there a problem of some kind with it?

    As to changing the control logic so that it only fires when a zone is calling — that's just a wiring change. Let us know what the actual valves are (make) and what controls you have now, and we may be able to give you the changes needed. Takes about an hour, and usually no parts required.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 8,771
    edited 12:55AM

    If the WM boiler is not leaking, then just update the control with this

    https://www.supplyhouse.com/Resideo-L7224U1002-120-Vac-Oil-Electronic-Aquastat

    It costs a lot less than a new boiler

    If the old WM looks like it is on its last legs and the old tankless coil flange bolts are rusting away and the burner is an ancient relic, then get any new boiler that comes equipped with a modern control system.

    If it is an old relic that is on its last legs like this with rust covering all the water pipe connections then replace the boiler with any new boiler that has a modern control

    If it is well maintained like this then just change the control.

    Note: maintenance guy in the photo

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HVACNUT
    HVACNUT Member Posts: 6,099

    Can you explain a little more? You want one thermostat to operate all three zones, or you want to only use one zone, leaving the other two disconnected or non operable?

    Can you show pics?

    Is the domestic hot water involved, or is there a separate appliance for it?