1988 Manufactured Home Needs New Furnace and Water Heater
I am in Sullivan County, NY (very cold) and have a manufactured house built in 1988, with original oil furnace (forced air) and an electric water heater.
I have experienced and heard nothing but disatisfaction with heat pumps in my area, so I'm hoping to find a different alternative.
Is there an oil or gas fueled system that will make heat (for forced air) and hot water (on demand would be fine)? Best would be a single unit to provide AC also.
Thank you.
Comments
-
Manufactured housing has special requirements for their fossil fuel burning appliances. the combustion air for the burner MUST come from outside of the enclosure. There are no oil fired boilers that make DHW that fit that criteria. However there are several oil and gas fired appliances designed for space heating that should be an exact fit for the duct opening where the old oil fired furnace was removed. There are also gas fired water heaters designed for manufactured housing. (Now we are talking about single wide and double wide one story manufactured housing where you leave the wheels under the actual building.)
If you are talking about Modular Homes that are built off site then 2 to 6 pieces are delivered to the site and a crane puts the pieces in place,on a prebuilt foundation, that is a different story. Modular houses and Manufactured houses are two different animals.
Nordyne has some options for you. Miller was a very popular furnace choice for manufactured housing in my service area. https://literature.nortekhvac.com/Miller/Gas_Furnace
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Other options for manufactured housing water heaters are specifically designed for this market. They usually have smaller tanks and the venting requirements are more strict and they must be convertible from Natural Gas to LP Gas (and back) so that they can be adapted to the gas that is available at the final destination.
Just about every water heater manufacturer has at least one offering available for this market. Here is one of Rheem manufacturing’s products:
It is available from Big Box stores and local Plumbing Supply companies.
The last idea for heat and air conditioning is the select a Package Unit. they are available in
- AC only.
- AC and Gas heat
- Heat pump
- Hybrid heat pump and gas heat (duel fuel)
Items 2 thru 4 will eliminate the need for a furnace inside the home letting you use that space as an additional storage closet, or making the bathroom or other adjacent room a little larger.
If you do not have access to Natural Gas or Propane Gas, and your only choices are oil heat or electric, then you will need to use the oil fired replacement furnace and an electric water heater. With Propane or Natural Gas you have many more options.
Hope this helps
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Um… well, I wouldn't have said Sullivan County was particularly far north, nor particularly cold — being well south of much of the State. Your design temperature is plus 3 F, and that is warm enough that a good high performance cold temperature heat pump should work. Mitsubishi hyper-heat units claim to work well down to - 5 F, for instance. So don't assume that a heat pump wouldn't be suitable.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you so very much!
You've provided lots of information that I was not aware of.
I need a little time to digest, but a couple of questions:
- I see do many posts on so many sites where everyone says how it is a slam dunk decision to change from oil to gas. But, I don't understand the case. I pay about $3.50/gallon for LP and about $4/gallon for oil.
- If I'm replacing the furnace I don't mind changing to gas — that way, I can use a separate on-demand water heater
- Will a package unit be able to connect to the existing duct work? Without some sort of indoor air handler where the current furnace is?
- Any chance a package unit can be a DIY project (assuming the DIYer is far from an HVAC pro, but very handy and eager to learn)?
Thanks!
0 -
On your question 1 — a lot of people can't do arithmetic. With oil for you at $4 per gallon, the LP would have to be less than $2.70 per gallon to get the same heat for the same price. LP doesn't have the heating value per gallon that oil does.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
That's funny.
So every $4 I spend on oil buys me 138,500btu while every $3.50 I spend on LP buys me 91,452btu (quick google gave me those numbers).
And, conversion to gas has an up front cost that would need to be amortized.
0 -
- I also agree with Jamie. If you have Natural Gas and compare it to your highest fuel oil bill they got in the winter, there may be a savings. However some folks look at a 2 to 3 months supply of fuel oil at $600.00 all at once and then compare it the the natural gas bill that comes in monthly and see that the highest bill is never over $200.00 (or something like that) and jump up and down to say that gas is cheaper. OR, someone who took out a 70 year old coal converted to an oil heater that operates at 60% or less efficiency, and compare that bill to a brand new medium to high efficiency gas heater and say that it saved them lots of money. But that is with Natural Gas. LP Gas is delivered just like Oil, from a truck. and the amount of energy measured in BTUs for a gallon of LP Gas (91,000 BTU) is a lot less than the amount of energy in a gallon of fuel oil (138,000 BTU). So when you have a choice between Oil and LP Gas of the same efficiency, Pick the oil heater.
- A tankless gas water heater will cost less to operate than the electric tank water heater you removed.
- YES you connect the package unit to the same ductwork. you use a collar made specially for mobile home duct work that prevents back draft thru the outdoor unit, from the furnace inside that will operate in the winter. You must also install a special damper made to be placed under the new furnace to prevent back draft in the summer. If you get a package unit that does both heating and cooling then you don't need that damper because you eliminate the inside furnace and just cover over the furnace opening with a sheet of metal and some mastic, then insulate over it. That is how you get the extra space inside.
- Package unit is most definitely a DIY job. The unit comes pre-wired and set up so you do not need to bother with refrigerants and for the most part, if it is already set up for LP Gas, then you can probably plug and play. I would have a professional from your gas company come and check your work to see that the flame is burning properly with combustion instruments. If you need to use a conversion kit to change the unit from Natural gas to LP gas, then you definitely need to call the gas supplier to do the start-up. You also want to save the Natural Gas parts from the conversion. You never know where that package unit is going to end up and if there is natural gas, you want that for sure.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Ed and Jamie,
As always you are both an amazing wealth of knowledge and a model of generousity for everyone.
I am encouraged by you to take on the DIY package project.
I actually have 3 manufactured homes each with nearly identical furnaces (1 has been converted to gas by a prior owner and 2 are oil). I don't have a philosophical or ideoligical bent towards any particular fuel type.
My biggest problem is they are all noisy and old. I don't know about the efficiency, but with nights in the 30's (F) they run for 20-25 minutes, stop (no call for heat) for about 40-50 minutes, and then repeat. In December-March, the no-call-for-heat times will be much less. I don't know what that tells us about the heating system.
An LP package system that uses LP for both heat and AC (correct?), and ties into the existing vents, would be very nice indded.
Any suggestions for a common 1000 sq-ft manufactured home?
Tankless is not a problem — I've installed about 15 of them so far (tiny number for a pro; large number for a homeowner — what that makes me is anyone's guess).
Thank you!
0 -
I don't know of any combination units fired by LP for heat and also providing AC — at least not all-in-one type things.
Your furnace cycle times tell you a lot more about the insulation in those mobile homes — which is probably pretty close to non-existent (at least the ones I've encountered were a little weak on insulation…) than they do about the furnace efficiency.
How cold does it get in the coldest months? If it doesn't get much below 10 F above, have you thought about possibly installing a heat pump? Might require a wiring upgrade… but it would give you AC as well as heat, and depending on your electric rates would be competitive to run. More expensive to buy.
1,000 square foot? I'm guessing a 70 by 12? The size furnace you need depends as much on where you are located (how cold it gets) as anything else.
One thing to consider: mobile home furnaces, in general, are slightly to significantly to a furnace for a regular house. It needs to fit in the space provided — which is usually pretty cramped — and still be serviceable. Most mobile homes (not all) also use a downflow furnace design, rather than upflow or horizontal which is more common in a stick built house, and may need more powerful blowers. Furnaces designed for the purpose, however, are easy enough to get.
Without knowing your heating requirements and how the present furnace is installed and ducted I can't get much farther for you.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@josephny, You can do the package unit for that home. Most places that provide parts and services for mobil homes will have a single package unit that operates on LP gas for heatingand 220 VAC for cooling. it is a very simple job because you connect the package unit to the under side of the ductwork with a collar that is made specifically for mobil home ductwork. Then you add a return boz in the loving room floor that will hold an air filter. both the supply and the return are 12" or 14" Flex duct from the package unit to the supply and return collars.
Here is a LP Gas 2 ton AC unit for you to research
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Here is a standard manufactured home double wide duct system
I have added the package unit and the flex duct connections to the supply and the return.
A single wide duct system is about the same except you just connect the supply to the bottom of the single trunk duct near the old furnace location.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I'm across the river from you in Dutchess county. Over here tankless water heaters don't fare well due to the quality of the water, personally I would avoid them. It seems like the higher costs of service and repairs and the need to be descaled often negated any energy savings. And they don't seem to last any longer either. A well maintained tank that has the sacrificial anode rod replaced when needed seems to last the longest.
As far as oil versus gas, no point in switching to LP in our area due to the prices. Natural gas is great, if available.
Most mobile home furnaces are Miller (Nordyne). I've heard Thermopride makes mobile home furnaces but I haven't seen any. The regular oil fired Thermopride furnaces are the best furnace you can get for a regular home in my opinion. They are built like a tank and last forever.
Heat pumps work fine until they don't. I like dual fuel heat pumps. That way if the heat pump fails and needs some special order part you still have a furnace to heat your home when it's approaching zero at night.
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements