what is this for

plumb1pa
plumb1pa Member Posts: 10

Two pipe steam residential home no air vents no pump, steam traps and F&T trap on some of the radiator returns. Do I need this?

Comments

  • Steamhead
    Steamhead Member Posts: 17,378

    That device IS the main vent. At the top you will probably find what looks like a cap, but is actually a check valve that lets air out but not in, forming a vacuum. This was a nice feature in the coal era.

    This is a Webster Vapor system. If there is a Return Trap at the boiler, it's the "Type R" system. If not, it's called the "Modulation" system.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    plumb1pa
  • Jamie Hall
    Jamie Hall Member Posts: 24,839

    As @Steamhead said — you not only need it, you have to have it! It's essential to the operation of the system!

    While you're at it, find a way to control the steam pressure to between 4 ounces and 8 ounces. You'll need a vapourstat.