EDR of this radiator
I have a small 6 tube radiator that 1 foot tall. Would 1 of yall have the specs for this radiator?
Located in durham NC.
Comments
-
Located in durham NC.
0 -
That's an unusual one. The short legs tell me it's probably a "small-tube" type. Check the section spacing- the distance between the center of one section to the center of the next one.
I've only been able to find 14-inch-tall rads so far. If the section spacing is 1-1/2" or 1-3/4", it's small-tube, about 24 square feet.
But if it's 2-1/2", figure on 32 square feet. This would be a large-tube rad.
Is this on a Vapor system?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
@Steamhead I don't believe so. I think this radiator was added later on as it's the only one like this on the system. The rest are normal tube radiators with a few column rads sprinkled in.
Would it be safe to guess on this one and throw in another 5-10k btuson the boiler to compensate for this radiator?
In that case, I'd need a 160k btu output boiler.
Located in durham NC.
0 -
32 square feet is 7,680 BTU per hour on steam. What exactly are we doing here? New boiler? Steam or hot-water?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
@Steamhead working on replacing the boiler. I actually miscalculated and if I'm correct the system should do good with a boiler with an output of about 210k BTUs. So a boiler with an input of 252k BTUs should do the trick.
Located in durham NC.
0 -
My calculations. Please correct me if I'm wrong
Radiator 1, 30 sqf
Radiator 2, 18 sqf
Radiator 3, 87.5 sqf
Radiator 4, 32 sqf
Radiator 5, 87.5 sqf
Radiator 6, 84 sqf
Radiator 7, 84 sqf
Radiator 8, 52.5 sqf
Radiator 9, 18.75 sqf
Radiator 10, 18 sqf
Radiator 11, 50 sqf
Radiator 12, 50 sqf
Radiator 13, 40 sqf
Total EDR with a 1.33 pickup = 867.4925
Total btu output of the system = 208,198.2
Boiler that should fit the system best would be about 250k BTUs.
Located in durham NC.
0 -
don’t do all that pickup and btu math, just compare your EDR to the sq ft of steam of the boiler
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
This. The Square Feet rating already has the pickup factor built in. Note that if the new boiler has a CycleGard low-water cutoff, which stops the burner for a level check every 20 minutes or so, you lose a percentage of output capability. I wouldn't try undersizing a boiler for this reason.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements