Navien NCB-240E - supply heating water temp?
Hello all,
I'm renovating a historic carriage house that's heated with a Navien NCB-240E.
Right now, this building has one circuit with a couple of cast iron radiators, and another circuit with fin tube base board. It never got very warm, because it was essentially an uninsulated garage.
I'm working on remodeling and insulating it, so it can be a guest house.
Total approximately 1925 square feet of heated space. About 625 of that is attic space (sloped ceilings).
I intend to have 3 heating circuits - the two existing circuits and another one for the attic.
I've done some heat loss calcs (which I intend to verify with a HVAC engineer friend). I'm hoping to use more cast iron radiators in the future, OR maybe modern aluminum radiators.
Regardless, I see that the BTU output of a radiator heavily depends on the supply water temp from the boiler.
What's the expected / desired SWT from this Navien boiler? I know the return temp needs to be below 130 deg F to condense. So should I expect 140? 150? out of the Navien? I have another property with a gas conventional boiler that runs about 180 deg, and would have no hope of heating the house at 150 deg, so I want to make sure I install enough radiator.
Comments
-
If you want it to condense, the output temperature needs to be less than 150 so you get the optimum 20 degree drop through the radiation — which should be sized to the average temperature (140), not the input.
However, you can set that Navien to go higher if need be.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I believe you can program it to sense SWT or RWT, so you have quite a bit of play.
0 -
the best first step would be a room by room load calculation. Next select the type of heat emitters, then size the emitters based on a 150 supply. If in fact the goal is to always run in condensing mode. It will take more radiation than a system running 180, of course.
Steel panel radiators are another option. Those design round a 30-35 degree temperature drop.
You need some solid numbers to design around
Outdoor reset should be involved also to maximize efficiency and provide long run cycles
This journal has good info on designing for lowest supply temperatures, and derate formulas for most heat emitters.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements