How can I find (and test) my steam system main vent?
Just moved. I'm trying to learn about my steam heat. Reading the Haloran book. He talks about clogged main vents or even guys replacing vent with a plug.
I have an old oil boiler. Finished basement. Pipes rise and go into the ceiling. How can I find (and test) my steam system main vent? How often does the basement finish have no clue about steam pipes and just covers the vents? How are they found when they get clogged? Thanks.
Comments
-
Finished basements are the worst. Your questions are good ones…lots of times the vents are closed off behind drywall.
Can you see any parts of your main(s)? (The mains are the big steam pipe(s) that run horizonally around your basement at the ceiling)
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Here is a video of my boiler
0 -
You have a dry return. It should connect to the main somewhere out in the system and since I don't see a vent at the boiler, the vent should be there. Looking at where the radiators are and where that return is heading (the pipe that connects at the bottom of the boiler) or a thermal camera might help figure out where that is. That piping would be wrong for a modern boiler but is probably ok for that 50's or 60's boiler. You or a tech should flood it to make sure it isn't leaking above the water line.
That insulation on the flue should be removed, it is not designed for those temps.
0 -
-
Here is more video. There are no exposed pipes beyond what comes into the walled off boiler room
0 -
It looks to me like that main starts in the boiler room, loops around the basement and re-enters the boiler room where it drops into the return. The pipes look to be the same size as they leave and re-enter the boiler room.
Check the last riser off the main before it drops to the return. That looks like 3/4" pipe and I'll bet there is a main vent screwed into it, just above ceiling level.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Need help decoding this.
Last riser off the main before it drops to the return?
A riser is a vertical pipe? The main is the horizontal pipe.
How can I find a riser if most of the main is hidden by walls/ceiling?
How can I find a main vent if its above ceiling level? Do I tear apart sheetrock just to learn about the steam system anatomy?
0 -
-
Last riser off the main before it drops to the return?
This use of “riser” means “pipe that goes from the main up to a radiator”
How to find it is why I dislike finished basements
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@CoachBoilermaker , it's the last tee with a pipe going up into the ceiling before the main drops to the floor. You might be able to shine a light up in there, or you might have to make the opening a bit bigger.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
I am having trouble understanding you. The last tee? What is the order? I have no idea what is first or last. The main drops to floor? Huh? I thought the main is in the ceiling. Can you tell me where to look in my video? Timestamp?
0 -
Where is the end of the main?
0 -
First tee is closest to the boiler steam supply — it's the radiator supply that is reached first by the steam. Last is at the other side of the main (the end of it). It is reached last by the steam.
The main drops to the floor via a vertical pipe at some point to let the water return to the boiler, which presumably is near the floor. The picture you posted isn't really applicable.
From :17 to :21 in your second video you are looking from bottom to top of the vertical "drop" that marks the end of one of your mains.
Your video isn't that helpful, it's probably not your fault because so much is behind walls and ceilings. But the majority of your video seems to be aimed at sewage and water lines.
You might have a vent on this little riser, seen at :24 in your second video:
Here at :28 I believe is your last riser to a radiator, at least on this main. I can't tell if you have more than one main.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
It goes by very quickly because you move the camera around so fast and so far- a common problem with these videos. But in the second video, you can see at 0:22, 1:59 and 2:23 where a 2" pipe elbows down at a 45° angle and reduces in size. That looks to me like the end of the main. From there, the pipe goes horizontal for a short distance, then drops and goes back into the boiler.
Now, at 0:23 in the second video, you can see a tee with a smallish pipe going up into the ceiling. At 1:25 you can see the same pipe coming up from the main toward a square hole in the ceiling, and a coupling screwed onto it. I bet your main vent is screwed into that coupling.
Having a steam main running around the perimeter of a basement is not uncommon at all. There is a neighborhood in Baltimore called Radnor-Winston where almost all the houses have this type of main.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
The end of the main would drop and connect into the bottom of the boiler.
It may drop to the floor and come up to a Tee called the Hartford Loop……or might just go into the lower tap on the boiler.
This is why still pictures are better than a video.
0 -
You guys are amazingly patient. Thanks.
Paul, I see the small riser at :24.
What am I looking for with the radiator riser at :28 ?
0 -
Don't worry about 0:28, he was just saying that's the last tee that actually serves a radiator.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
When the heat is turned on, I should hear venting at that :24 small riser?
0 -
-
Now, @CoachBoilermaker , next step is to measure the length of the main as it runs around the basement. I think the pipe size is 2-inch, the outside diameter would be a bit bigger than that.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
-
-
Why do we want to know the total length of the main?
Not sure that's possible, as it's hidden in the ceiling anyway
0 -
Will the basement main have 6 risers direct to each radiator
Typically one for each radiator yes
The steam heat system is in good working order from what I was told. So, I assume the vent should be working.
Bad assumption! and if they can't even see the vent, how can they report that it is in good working order?
Why do we want to know the total length of the main?
Not sure that's possible, as it's hidden in the ceiling anywayBy knowing the size and length of the main, you can get a good idea of the amount of main venting you should have. But really any is better than none. A lot better than none. But I'll bet you'll be told that a Gorton #2 is a good start.
When the heat is turned on, I should hear venting at that :24 small riser?
No, main vents are often too quiet to hear unless your ear is basically next to them…if they are even working as others indicated.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
You can buy Inspection canmera's for $20 or so that have long 3/8" flexible probes and a screen that are designed to inspect inside of wall cavities and even piping. They have LED lighting so you can see what's inside dark places.
One of these would save a lot of work compared to tearing a ceiling apart.
Bob
Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
It is starting to make sense now. That small riser at :24 must be the vent. What else would it be? Radiator risers are bigger. Plus, it's near the very end of the main.
Another thing I realized. There was an addition on this house. Added dining room and 2nd floor bedroom. They had to add risers to go to these 2 new radiators? I will look to see if there is a branch of main that goes under that side of the house.
Thanks to the guys in this thread. You are generous with your time, experience, and patience.
1 -
-
There is a round copper thing at the top of the small riser at :24 !!
This is a main vent, right? Looks like a Gorton?
The nut seems flush with the sheetrock, so I'm not sure how you'd swap it out, can't fit a wrench there.
Could this mean the main vent predates the sheetrock?
0 -
Yes it looks like a Gorton #1. Yes it might pre-date the sheetrock.
You can tell if it's properly letting air pass by seeing if the pipe leading to it gets steam hot shortly after the main below it gets steam hot
Then you might be able tell if it's properly stopping steam by carefully reaching up there and seeing if it is letting hot steam out.
Alternately, you could put a pipe wrench on the 3/4" riser pipe and remove it. Then blow into the pipe with the vent upright. It should pass air. Then flip it upside down (vent at the bottom of the pipe) and blow into the pipe. The vent should block air.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Agreed- Gorton #1. Did you get a chance to measure the length of the main? if it's more than 20 feet or so, you'll want to upgrade.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
In other words, if air is passing correctly, what gets hot before what?
0 -
the C side first, heat should flow from the C side. You should be able to feel it travel along that main.
Then it should pretty quickly flow up B. Then the vent up there should close, allowing no steam to escape.
The A side should not get hot (at least not very far and not very hot), since there's no where for the steam to go after the vent on B closes.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
The only way to properly test any vent is to blow cold air through it in its operational position, then have steam go through at under 2 psi to see if it closes.
0 -
Not following the part about "A" staying cold.
Steam reaches C. Then goes up B. Main vent closes. Does B get "full"? Won't more steam from C now reach A since B is full of steam (and vent closed)? Or am I making the mistake of assuming steam flows like water? Does B not actually get "full", and then diverts new steam towards A since B is full? Doesn't work that way?
0 -
Steam reaches C, then goes up B, main vent closes. We are all good to this point.
Does B get full? Yes, B gets full of steam.
Won't more steam from C now reach A since B is full of steam (and vent closed)?
No because there is currently air in A all the way to the wet return/boiler where it ties in. The air won't let the steam go by. And the air will stay in there because there is nothing, no vent, to let it out.
The reason the air gets to C and then B is because the vent at the top of B is letting the air escape (that is the vent's whole reason to exist in fact).
Steam does flow kind of like water, but more like air since they are both gases. Steam flows from high pressure to low pressure, and at B there is high pressure so the steam won't flow there.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Water and steam are not both gases, they are both fluids ( sorry for getting off topic)
-1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements