Injection Mixing for In-Floor with Baseboards
I'm replacing a 30year old boiler with a LAARS FTF. The system utilizes baseboard and in-floor concrete radiant. The copper riser from the horizonal supply and companion G-1558 are designed to inject return water Lleft riser) with hot boiler output (Right). My question-
"Without a check valve on the L-Riser, won't the main supply receive cool return all the time and dilute the boiler output to the main supply?
Comments
-
Nice press connection work. Pity that it makes absolutely no sense at all. And a check valve isn't going to help.
The principle is sound — and used all the time for radiant floors or the like taking their hot water supply from a primacy manifold. But. To make it work, there is a line from the return from the floor (there is also a line connecting to the primary manifold) to the cold inlet of a thermostatic mixing valve (it's nice if that can be controlled by an outdoor reset). There is a line from the primary manifold (the boiler circulation loop) to the hot inlet of the mixing valve. The output from the mixing valve goes through a pump and on to the radiant floor.
The baseboards are their own secondary circuit, with either zone pumps or zone valves and a single pump, coming off the primary loop manifold and the returns going back to the manifold in the usual primary/secondary way.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I can't see enough of the boiler piping to see what you have.
Here is a common way to do a simple primary secondary, a mixing valve is a better way to blend down temperature. What you have would need a couple valve, one in the cross over, one on the supply. Then you adjust to get a desired temperature.
Know as a dumb mixing concept because it has no way of knowing or adjusting output temperature. A thermostatic mix valve would, however.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements