Head loss for manifolds
sriche01
sriche01 Member Posts: 29
Quick question: When calculating head loss for a radiant loop, do you add the pressure loss of each loop together, or is it just one loop that is taken into consideration?
Thanks!
  • sriche01
    To be clear, I mean a manifold of multiple loops in one zone…
    It is the pressure loss in the one loop with the greatest loss. The pressures do not add up — but the flows do.
    GGrosssriche01
  • GGross
    GGross Member Posts: 1,941
    to add to that, you will have pressure drop for the supply and return piping, valves, the manifold itself, etc. you will add the pressure drop for all of the supply and return piping system and manifold, to the head of the loop with the greatest pressure drop. That will be your total head, then add the flow requirement for every loop on that manifold, that total flow, and total head number is your pump spec, assuming you are individually pumping that manifold.
    sriche01
    hot_rod Member Posts: 27,707
    The manifold will have some flow resistance, Caleffi shows 1.23Cv for combined S&R. So very small amount
    On a high flow 3/4 snowmelt, you may want to run the pressure drop calc, and include that pressure drop of the circuit. And the glycol derate..
    sriche01
  • sriche01
    Thanks guys! I appreciate the repsonses!