Can anyone please help identify the main vent in the picture below? There are 2 additional vent holes on the other sides the same as in the picture.

For extra context, I'm in the process of replacing the main venting on my single pipe steam. This all after a boiler replacement and new radiator vents last year.

Currently I have two mains (53' of 2" and 34' (8' of 2" and 26' of 2-1/2")). The long main will get a combination of Gorton #1, #2s or MOM #1 to replace an existing big mouth which was spitting/not closing.

The short main has the vent pictured behind drywall so I'm trying to assess whether to remove it or leave in place to get reasonable venting across both mains.

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,339

    That's a crappy old Somethin.or other. You wanna go with Gorton or Hoffman. Mad Dog 🐕

    mattmia2
  • gt873923
    gt873923 Member Posts: 22

    😄 Thanks @Mad Dog_2

  • gt873923
    gt873923 Member Posts: 22

    I'm probably going to do a Gorton #2 on the short main and then 2 x Gorton #2s on the long and see how that does.

    Mad Dog_2
  • Steamhead
    Steamhead Member Posts: 17,133

    It's a Dole #4- pathetically inadequate for the main it's on. Use a Gorton #2 at the end of each main.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2
  • Neild5
    Neild5 Member Posts: 170

    As an FYI, the Big Mouths are rebuildable, there is one oring. I replaced i

    them once 6 years ago and they all have been fine since. I have 10 Big Mouths on our system.

    Mad Dog_2CLamb
  • gt873923
    gt873923 Member Posts: 22

    @Steamhead thanks, good to know what it is. Will replace with a Gorton #2. Do you think one will be enough for each main or should I go with 2 on the longer one? I also have a MOM #1 I can add on as well.

    @Neild5 thanks! The folks at B&J actually sent me a new internal which I've installed (o-ring actually looked OK). I may test out the big mouth again but just wanted a backup in case the new internal doesn't fix things.

  • Steamhead
    Steamhead Member Posts: 17,133

    @gt873923 , start with one #2 on each main. You want the mains to vent to the end in a minute or two, measured from the time steam starts entering the mains at the boiler end.

    If they vent unevenly, add the M-o-M to the slower one. If that doesn't do it, add the Big Mouth.

    Once this is done, every radiator takeoff will get steam about the same time, helping to bring the system into balance and reducing the boiler's running time.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2
  • gt873923
    gt873923 Member Posts: 22

    @Steamhead got it, thanks again!

    Mad Dog_2
  • gt873923
    gt873923 Member Posts: 22

    Progress has been made. Got the dole #4 off the short main. Trouble now is working out how to get the necessary main vents on due to a lack of headroom and the old coupling and close nipple not budging. As it stands I'm considering a few options:

    1. Fight the old nipple and couple off then install a Gorton 2 straight up behind the drywall. This should give me the extra inch a half I need for the Gorton.
    2. My preferred. As 1 but install a street 90, then 12 inch nipple outside the drywall then a 90 before the Gorton.
    3. Some kind of arrangement off the existing stuck nipple behind the drywall (with access panel) and using more smaller vents like 3 Gorton/MOM #1s.

    I've hit the old coupling with PB Blaster and a right angle pipe wrench to no avail. A cheater bar would be my next step. I'm reluctant to try heat as there's a whole bunch of wood and Plywood surrounding the pipe.

  • mattmia2
    mattmia2 Member Posts: 10,140

    Stick a rod or a small pipe inside the fitting before you really wrench on it so you don't collapse it

  • Steamhead
    Steamhead Member Posts: 17,133

    If that coupling doesn't come off, use option 2. Make sure the 12" nipple pitches back toward the steam main.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • ethicalpaul
    ethicalpaul Member Posts: 5,881

    I sure do hate finished basements

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 10,140
  • gt873923
    gt873923 Member Posts: 22

    Thanks all, will keep you posted on how I get on. I can get a recip with a carbide blade in there so that's an option as well but some care needed to not make things worse.

  • Steamhead
    Steamhead Member Posts: 17,133
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 10,140

    You could also use 2 street 90's at each end and make swing joints to pitch the lateral

  • gt873923
    gt873923 Member Posts: 22

    I've been slowly attacking this remaining nipple but run into some issues. My cutting of the nipple in order to free it up has left me with a broken nipple as I didn't manage to cut far enough down the fitting in my various attempts. I've tried hacksaws, oscillating tool, cold chisel, nipple extractors to no luck. I'm only working with 8 inches of vertical room and about 1-1/2 inches horizontal to the foundation wall so tricky getting even a mini hacksaw in there.

    Trying to work out what my options are here as cold weather gets closer. I'm thinking of:

    1. Continue hammering away at the broken nipple in the hopes it comes free.
    2. Plug the hole somehow then drill and tap a 1/4 hole further back on the main for a new place for the main. See pictures for current config.

    Open to any ideas though on alternatives!

  • Steamhead
    Steamhead Member Posts: 17,133

    You might be able to tap the inside of that broken-off pipe for 1/2" pipe thread. It'll work just like a face bushing.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmia2
    mattmia2 Member Posts: 10,140
    edited 4:16AM

    cut 2 little slits in the nipple almost to the threads then pop out the piece in between with a small chisel. Might use a reciprocating saw blade in a mini hacksaw frame, there are some that are very narrow.

    use some fittings to get the vent outside the wall so someone can find it later. if you can't screw something in there you will probably need to make a bigger hole and cut out that fitting and the riser and replace it. some of that being copper wouldn't be terrible.

  • gt873923
    gt873923 Member Posts: 22

    @Steamhead thanks, that's a good idea. I'll give that a try and see how I get on.