3/4" to 1/2" to 3/4
I was wondering if I should I rebuild this section here so everything is 3/4" or is it ok like this?
The Backflow preventer is also corroded. I'm assuming I should replace this part and if so I was thinking I could get 3/4" if I needed to replace this section entirely. Then, I'd have to buy a new flow regulator.
Thanks in advance,
Anthony
Comments
-
Not absolutely necessary, but yes, you can certainly clean it up. I'd like to see you get rid of the black pipe as it is prone to corrode and form a solid block of rust inside. The reduction and then increase in pipe size is no big deal. If you feel motivated, I would also pipe a bypass around the fill valve for easy purging and pressure control.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
In your case since it looks like you have a lot to purge if you ever drain the system I would do the manual bypass that @Alan (California Radiant) Forbes shows in 3/4" and I would put a manual valve after all of it where it connects to the system so you can service the PRV without draining the system.
The 3/4" and manual bypass will let you get more velocity to purge the air out.
0 -
-
Thanks, everyone.
@Alan (California Radiant) Forbes I am draining the entire system in the coming weeks so any work like this will be done if it's recommended. So I can better understand the point of the bypass… Like @mattmia2 mentioned, is this strictly to get more velocity to purge the air out faster/easier? Where does pressure control come into play with this?
I'm new to this, is it more difficult to purge the system while the backflow/fill valve is inline? I'm guessing it hinders the flow?
Also, I have a good bit of Black Iron just above section too shown below. While I have the system drained, would it be a good idea to get this all to 3/4" copper?
My current plan is to plumb a new zone off the left side there and add a Purge Valve (this one here). Maybe I'll just buy three of those valves and re-build that entire area with 3/4" copper?
@mattmia2 Since there's a shutoff valve above the PRV already, are you saying to have one below and above so I can close both off and service the PRV/Back Flow Preventer?
I'm guessing I'm looking for something like in diagram B below?
Here is the system as a whole. Currently, the Back Room zone is not in place.
0 -
Diagram A is what you'd want. The isolation valves are just for service of the prv assembly. You may have existing valves that serve that function, I can't see all of the system from your pictures.
The bypass is just for purging, 1/2" is fine for the prv itself. Most systems do fine without the manual bypass but I can see where it would be easier than dealing with the fast fill lever on the prv(or auto fast fill) and more velocity might make purging easier depending on what your system is like and if you have a purge enough drain in the system to purge through without building up enough pressure to open the relief valve. You woudl watch the pressure gauge on the boiler and throttle the bypass valve to make sure it doesn't get to 30 psig and open the relief valve.
Black iron is fine in the hydronic heating side because there is no fresh oxygen in the system to continually corrode it like in a potable water system.
Is that pex the potable water system?
1 -
@mattmia2 As you can see in this diagram of my plumbing system, I don't think there is any valves before that section. Only one valve after it. Also, you can see I do have some purge valves on the individual zones.
I haven't done too much research on purging just yet so you did lose me a bit half-way through the second paragraph above. But, I'm guessing I will need to learn how to purge once I re-fill the system…but, it seems like plumbing in the manual bypass won't be hard to plumb in so perhaps I'll just add this to the system and learn how it all works after haha!
Regarding the PEX. Unfortunately, yes, my potable water is all 1/2" PEX. Thoughts on that?
The runs aren't overly long; I could prob replace it with 1/2" copper easily. I just bought this house (first time homebuyer) so I need to pick my battles here for now.
Although, water is of utmost importance to me considering I'm a transplant recipient and I am immunocompromised so I'm interested in your opinion on that.
Here is my entire system currently:
0 -
Pex is fine for potable water. I wanted to make sure that wasn't for heating because it looked like it probably wasn't the oxygen barrier version of pex that you need on a hydronic heating system.
If you shut off this valve before you work on the prv you shouldn't get enough air in the system that you will need to purge it.
I would add a valve here so that you don't have to shut off water to the rest of the house to work on the prv:
0 -
-
-
You don't want to pump at the expansion tank, move the tank to that lower tee before the circ pump.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hey, @hot_rod, could you elaborate? Moving the expansion tank was not on my agenda (at least this summer). So far, I added a new zone, replaced backflow preventer, rebuilt circulator pump with new gaskets, and replaced some leaking valves.
Here is how the system looks outside of the schematic diagram. Sorry for the mess.
Could you help me with what you mean by "You don't want to pump at the expansion tank, move the tank to that lower tee before the circ pump."
The "lower tee before the circ pump" is the T right above the pump in the photo below.
0 -
Physical location is not relevant here. What is relevant is hydraulic location — that is to say, the sequence going in the direction of flow in the system that things are placed in. In your system the sequence is circulating pump, boiler, expansion tank — and that is the problem. You want the expansion tank to be on the INLET side of the circulating pump, so the sequence would be expansion tank, circulating pump, boiler. If your diagram is correct, there is a T just before the pump — on the inlet side — which has one outlet plugged. If you rerouted the expansion tank inlet to that T from where it is connected now, it would be much better. Like very much better. You don't have to move the tank — just run the pipe from it to that T before the pump, rather than where it is now. Looking at the picture, that may be somewhat easier said than done… but it could be done.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Okay, I was not planning on this project, but if it's better this way, I will certainly consider the change. Is it safe the way I have it if I leave it until next spring/summer? Or should I take care of it before this upcoming winter?
I don't think I understand what you mean by re-routing the tanks inlet side to the plugged T outlet. Does the tank not need to be inline with the system? Here is a different angle of the circ pump and the T that's about it. Are you saying something like this?
0 -
The green air purger stays where it is
The tank screws out and reconnects to this tee just above the pump, along with the gill valve connection
Use pex or 1/2 copper to locate the tank elsewhere if you need, but moving the tanks connection to that tee and you are pumping away
The air scoop is fine where it is, still close to the hottest temperature
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@hot_rod thank you.
Not sure I'm following 100%.
So, you're saying to leave the air scoop where it is, so I'm assuming I would plug the bottom of it? And, leave the top that's on top?
For the tank, am I simply running it directly off the tee like this drawing below? The specs on the model tank I have say it can be installed horizontally. Could I just do that horizontally on the right side of the tee like in the second photo? Do either way work?
Thanks,
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements