rooftop unit trane
creger.robert
Member Posts: 40
have 12-1/2 ton rooftop unit trane r22 has 2 circuits
one circuit running fine
2nd circuit high head low suction like a restriction-did frost test freezes at orifices on this circuit
does not freeze at orifices on circuit running fine
0
Comments
-
Plugged filter drier? or plugged orifices
0 -
Plugged orifices are really common on those - especially if they have been a little abused with dirty condensers.
0 -
filter drier has been changed
0 -