The case of the leaking 7 year old steam boiler this Fridays case
The brewery shuddered its doors suddenly, letting at the employees go. Everything was left as it was. Fast forward nine months and the new owner is looking over the equipment and called us in. We discovered several tubes were leaking and the boiler was only 7 years old. Prior to shutdown, the old brewmaster had a water treatment program and was diligent about it. What caused the tubes to fail? I will let you know Friday at 6am EST
Respectfully
Ray
Boiler Lessons
Comments
-
The best outcome for the boiler would have been to drain the boiler and store it totally dry or the second best case would be to fill the boiler to the nozzle, add the proper amount of treatment to store the boiler, and heat the water until it steamed and then close all valves for total isolation. My guess would be that they did neither of these and instead just shut off the electricity and left the boiler filled to the normal water line. During the shutdown oxygen ladened water entered the boiler through a leaking feed valve or bypass valve and ruined the tubes. You did not say if the tubes went bad internally or externally but if they went bad from the outside then the tubes could have been excessively sooted and the humidity in the building was high and could have produced an acid that ruined the tubes.
0 -
Too much MU water would be my guess. If they take on a lot of MU water it should be heated.
0 -
It was a Burnham?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
If the boiler was off for 9 months there was plenty of opportunity for air to circulate through the system and add oxygen to the water to rust the boiler, especially at the surface of the water.
0 -
I guess if I have to explain a joke, it's not funny 😂
Thanks Ed!If the boiler was off for 9 months there was plenty of opportunity for air to circulate through the system and add oxygen to the water to rust the boiler, especially at the surface of the water.
What would allow air to circulate in boiler?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
The various venting in the system. If there is no steam then the steam traps will be open. whatever path that the air uses to get out will be open to the atmosphere.
0 -
Boiler was partially full of water
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
If that was a concern, wouldn't all boilers rot out every summer?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Happy Friday
The reason the boiler failed was the water was laying in the boiler for 9 months with no chemical treatment. It caused oxygen pitting and it turns out several of the tubes were leaking. The brewer had to retube the boiler.
Ray Wohlfarth
Boiler Lessons0 -
And/Or however it was operated during the rest of its lifetime—there is no data as to the condition of the tubes when they shut it down.
I ask again out of my own ignorance, and for my education, if 9 months of sitting rots out a boiler how do boilers survive the summer? Are the steel boilers a lot more prone to rotting out with water sitting in them vs cast iron? Do all steel boilers have treated water?
PS: you kind of tricked us with this question Ray 😀
You said
> Prior to shutdown, the old brewmaster had a water treatment program and was diligent about it.
So some gremlin drained the water treatment that must have been in there from when the brewmaster shut it down on his last day and replaced it with extremely caustic water instead?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
It would seem to me that if the water was treated and if the boiler had been run to drive out the oxygen than it should have been ok for 9 months.
Most would recommend either filling the boiler before shutdown (wet layup) or draining it before shutdown (dry layup)
Steel boiler can last a long time even on steam. I would suspect the tubes were compromised before the shut down
1 -
@ethicalpaul I did not mean to trick you. We were at the brewery about two months before closing and didnt see any leaks When I spoke with my water treatment tech, he blamed it on the lack of water treatment
@EBEBRATT-Ed The tubes may have been leaking prior to the shutdown
Ray Wohlfarth
Boiler Lessons1 -
Before I retired in 2007, some of the "fly by night" companies would sell boiler tubes made in China. They were garbage and did not last very long.
0 -
@retiredguy I never knew that but have seen the nipples made in china fail within a year
Ray Wohlfarth
Boiler Lessons0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements