Point of use hwh
![RayH](https://secure.gravatar.com/avatar/0a650ef9822e061a8a237f379cb3bcb2/?default=https%3A%2F%2Fvanillicon.com%2Fc469f26d9b3c3526a3dae565b2971948_200.png&rating=g&size=200)
I have a customer with a small 110v plug in point of use water heater that services one bathroom lav sink.
For some reason it needs to be replaced about every 6 - 8 months or so.
The water here in Florida is pretty bad and the guy has a water softener to get rid of all the sediment. So I can eliminate that as an issue.
Not sure if it could be electrical or something else that I'm missing? Any thoughts on the topic 🤔
Comments
-
Hi, Is it a glass-lined tank? If so, softening is what may be doing it in. Over-softened water can quickly eat up the anode in the tank. You want to leave 60 to 120 ppm of calcium and magnesium hardness in the water after softening. A clue that the anode is working too hard is gas at the tap on first use. Also, check pressure. 40-60 psi is best. It could be electrical also, so you have a few things to look at. Is the tank grounded? Is there a jumper between hot and cold lines if they are metal?
Yours, Larry
2 -
The anode rods in the POU tanks typically is tiny…like pencil.
0 -
Open one up & see what's going on with it.
0 -
The hot and cold supply lines are 3/8" braided steel. Not sure if they need a a ground connection between them?
0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements