The case of why are the pipes banging, this Fridays case.
In this case, the brewer said his pipes were banging. This is the steam header. I identified three things wrong. Just curious what you see. I will post the answer Friday morning.
Boiler Lessons
Comments
-
Here is what I see, although a wider picture would be helpful. On that installation, I would prefer a header drip trap be installed on both ends of the header, a full size condensate drain fitting the same size as the header be welded to the bottom of the header to collect the condensate, if that is not how it is now installed, a longer vertical drip pipe, a tee instead of the elbow and a drain valve off the tee to flush out the drip pipe, and a stop valve after the discharge tee for future service of the trap or check valve. I would also guess that the trap's condensate handling capacity is too low especially on a cold system startup. Another item, although some may dispute this comment; removing some or all of the insulation on the line after the trap to allow for the condensate to cool.
Boy, that is a sloppy job of pipe insulation, I would not be proud of that.
0 -
I have heard some very loud swing check valves make some very loud banging noises when added to a system.
I see something that might have been recently installed. Did the banging start recently? Is that a swing check recently added? It looks new and not insulated like all of the other pipes. This is my first thought as to the source of the banging. Not to mention the condensate backing up.
0 -
1- The drip line from the trap has a water pocket- it needs to slope down from the trap all the way to the return line.
2- The strainer before the trap should be facing to the side instead of straight down- another water pocket.
What pressure is this system running?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
Drip to trap may not be large enough
Trap discharge is lifting condensate
trap to close to bottom of header
These 3 things are causing water to back up into header especially on a cold start before you have enough steam pressure to lift the condensate.
None of the above three problems are fatal mistakes on their own but 3 of them together in one spot is 3 strikes and you're out.
0 -
Wow you guys were awesome If I had a star I would put it on your foreheads. LOL
@EdTheHeaterMan The beer didnt turn out. There are other issues I will share at a later time.
#1 is the condensate pipe is too close to the steam main
#2 is they used a concentric reducer instead of an eccentric reducer
#3 is the strainer should be piped with the blowdown horizontal and not straight down
#4 is the condensate pipe rises and creates a water seal.
Here is the video link
Ray Wohlfarth
Boiler Lessons3 -
-
-
Nice video. Can you elaborate a bit on the swing check? Is it also part of the problem of making noise?
0 -
2 could be solved with a reducing ell….
0 -
Thanks for the Sarco info. Never heard that before and have never seen one installed that way
1 -
@Intplm. The check valve is used after the steam when you are lifting condensate. It's not needed if the condensate drops or pitched away.
Ray Wohlfarth
Boiler Lessons0 -
Yes, agree. I was thinking that this check valve was a part of the banging noise issue.
0 -
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements