4" gasketed SDR 35 after sewage grinder

Zman
Zman Member Posts: 7,611

I am working on a project where an existing home is having a sewage backup issue on the service line between the house and the main. It turns out the utility contractor that installed the stub to the lot prior to the house being built ran the line dead flat. Because of the existing elevations between the house and the main, there is no way to fix the problem. A contractor is now suggesting adding a grinder station just outside the house but says that the existing 4" SDR 35 gasketed pipe running to the main needs to be replaced with pressure pipe. I totally get that if there was any vertical head involved he would be correct. I just can't see 10 GPM or so running through a 4" flat pipe building any pressure. I think that 4" SDR 35 is good to about 5 #. Any thoughts?

"If you can't explain it simply, you don't understand it well enough"
Albert Einstein

Comments

  • ChrisJ
    ChrisJ Member Posts: 16,393


    Best I could find is it's considered gravity sewer pipe and therefore has no pressure rating other than it's stiffness rating.

    To me that means no one will say it can handle any positive pressure at all regardless of what it could actually do real world.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 11,307

    i mean my thought would be to run the pipes above the floor in the basement if you had to to avoid having an ejector pump…

  • ChrisJ
    ChrisJ Member Posts: 16,393

    I didn't see any mention of a basement or where the main drain and sewer connection is in reference to it?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Zman
    Zman Member Posts: 7,611

    The house is slab on grade and the piping in the interior slab cannot be changed. The issue starts outside the building. Neither the pipe leaving the building nor the sewer main can change elevation. The line plugs up every few years due to the lack of slope of the pipe. A much cheaper option would be to set up an motorized valve on a timer to dump a slug of water down the drain on a schedule to clear the line.

    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,659

    If it's occurring only every few years, I would cut in a full size wye with clean out as far back to the foundation of home and flush from the nearest fire hydrant with a 2 1/2" hose every 6 months. Work it out with your Local FD and make nice. Mad Dog

    Zman
  • hot_rod
    hot_rod Member Posts: 24,070

    There is no pressure rating on ASTM D 3034 PVC.

    How long of a run? Could you push a 2" schedule 40 inside and pump to the main where it is a pitched gravity.

    Someone makes a pump capable of that.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 11,307

    I come from the land where things under ground have to start at 40" if you don't want them to freeze.

    I considered sticking polyethylene or something inside my orangeburg until it got to the clay stub at the main and using a pump.

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,659

    What state are you in, Matt? Mad Dog

  • Intplm.
    Intplm. Member Posts: 2,342

    Hey there @Zman

    Have you considered using the current SDR pipe as a sleeve and installing a smaller diameter pipe inside creating pitch from within?

    If this is possible you could either go without a pump depending on the pitch or use a conventional sewage pump, depending on the orientation/ distance of the run.

    Zman
  • Zman
    Zman Member Posts: 7,611

    How would you adapt the pipe at the tap? I could see how you could use a reducing furnco or modified glue reducer on the pump end. Would you just let the tap end sit inside the pipe and figure most of the water will go into the main?

    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Intplm.
    Intplm. Member Posts: 2,342

    You would only need to adapt, or install at your end, or that is the pump side and send the discharge, smaller pipe, open and dead-ended to terminate when it finds the main to discharge into.

    A proper fit at the pump discharge should do the trick.

    From here I cannot be too specific of course, but if you have the room, it can be do-able.

    Zman
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,659

    Upper or Lower Peninsula? Mad Dog

  • mattmia2
    mattmia2 Member Posts: 11,307
    edited June 2024