Case of the random midnight no heat call, this Fridays case

RayWohlfarth
RayWohlfarth Member Posts: 1,668

In this case, the customer said they had no heat at night. It would happen every few days. The building had a control system that allowed us to track the boiler starts and stops and the hydronic loop temperature. The control system showed the loop temperature dropping and it was calling for heat. This led us to the boilers. They were reading standby which meant they had no call for heat. We replaced the relay that was used by the control system to enable the boilers. We still had issues. I will post the video on Friday morning

Regards

Ray

Ray Wohlfarth
Boiler Lessons

Comments

  • ratio
    ratio Member Posts: 3,816

    Hmmmmmm… Not a lot to go on, but I'm guessing something was tied in to a light switch.

    PC7060CLambIntplm.
  • Alan Welch
    Alan Welch Member Posts: 270

    The thermostat was located above a lamp on the desk of the nighttime custodian.

    EdTheHeaterMan
  • RPK
    RPK Member Posts: 119

    So you confirmed that the control system is calling for heat at the very same time the boiler(s) are not getting the command. My first thought was that there could be a timer wired in series with the enable output. I ran into that exact scenario years ago with some newly installed Lochinvar Crests that the electrician powered via a lighting panel. Turns out the whole panel was powered via a contractor that was on a timer. We figured it out because the outtages were at regular times down to the minute.

    I don’t think you’re dealing with the same thing in your example. In the trend log you shared it shows the supply temp dropping at different times. In fact, the 12/21 temp drop appears to have occurred about late morning. The December 24th drop occurs at night. This is contrary to the title which references midnight….

    I’m down to a few possibilities:

    1. Intermittent bad output on BMS controller
    2. Intermittent control wire connection between BMS controller and boiler

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,668

    The midnight title was something I should have named nighttime I guess. Sorry. We would get random calls in the morning saying the heat went out at night. Anyway, I digress. The cause of the issue was although the building controls called for heat, the internal relay would work sometimes. We disconnected the boiler and used the boilers control system to control the boilers and the morning calls ended. Here is the video.

    Ray Wohlfarth
    Boiler Lessons
  • mattmia2
    mattmia2 Member Posts: 11,107

    The relay in the BMS?

    They have the same problem with if the mechanical design of the board isn't good the solder will fatigue and break just like any other relay…

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,668

    @mattmia2 I never had one do that What's strange is that it only did it occasionally

    Ray Wohlfarth
    Boiler Lessons
  • mattmia2
    mattmia2 Member Posts: 11,107

    The solder cracks from the little bit of flexing every time the relay makes or breaks then that crack sometimes makes a connection, sometimes not. It is really common in appliances. It can happen to the contact or the coil connections.

  • JoeEngineer
    JoeEngineer Member Posts: 19

    not for anything but why does the display indicate "Chiller Load Response?"

  • ratio
    ratio Member Posts: 3,816

    It's a trend log with all the other points turned off except one of the water temps.

    I make lots of these, tracking all sorts of stuff on the same screen. It makes diagnostics much easier to see everything at once.

  • Intplm.
    Intplm. Member Posts: 2,267

    I'm wondering. Grasping at straws here, but could there be a dead spot in the motor?

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,668

    Thank you all. It turned out the building controls and the boiler controls didnt like each other.

    Ray Wohlfarth
    Boiler Lessons
  • pell
    pell Member Posts: 23

    Seems to me it was working correctly. That's why we put these overpriced and over rated controls, on to save fuel, correct?

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,668

    @pell I am not sure if the two control systems were fighting each other but as soon as we disconnected them from each other, the system worked.

    Ray Wohlfarth