A mix of pex fittings and pipe.
Expandable PEX -A- with the expansion collar. Has anyone used the [ fitting ] with the expansion method with a crimp connection? If so, did it fail?
And has anyone used fittings meant for the crimp method with the expansion method fittings?
Has anyone used the PEX -B- using the expansion method? If I'm not mistaken Sioux Chief has come out with a PEX -B- that can be expanded. Is this also being used?
Comments
-
I have crimped pex A without issues.
I don’t see how a crimp fitting works after you expand the tube? The crimp fitting fits inside the tube already
Yes several pex B manufacturers allow expansion
The official answer lies in the listing numbers on the tube, and fittings, you can find all that and more at the PPI website
Early on pex manufactures claimed to void the tube warranty if you used fittings other than their brand
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Why don't you use the Viega fittings like @kcopp suggested and that you commented on?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Uponor pex can safely be crimped, expanded, sharkbite, you can't use an F1960 fitting with a crimp collar though, because the pipe needs to be expanded to accept the f1960 fitting, it won't just slide in there, and then once expanded the crimp ring won't be the right size.
Sioux chief does make a Pex-B that is approved for F1960 (cold expansion) fittings. I know many people who use this without issue.
0 -
I do use Viega and Uponor. I'm wondering if others have used mixed fittings etc. with different joining methods.
Expansion uponor, that fitting. Has it been used to crimp pipe with success? I haven't and wouldn't try it blindly.
@Alan (California Radiant) Forbes your post ( thank you for showing it again,) was part of what I was thinking about when I started this conversation.
I have used both methods, expansion, and crimp. Has anyone interchanged the fittings?
As to the tubing. PEX -B- was not recommended for expansion till recently. or am I misinformed?
1 -
This all sounds cut and dry for many folks, but you need to understand that not every application is new construction using all new tubing. Some of us do repair work on existing equipment that has other than our standard product already existing in the home/building. This is a good question that many would like to know the answer to. Wouldn’t it be nice if there were only one standard for PEX tubing and there was no such thing as PEX-AL-PEX or PEX-a or PEX-b or QUEST or that rubber ONIX stuff. Then there would be only one fitting design and this question would not need to be answered.
I like the fact that there is a place to look that stuff up
“The official answer lies in the listing numbers on the tube, and fittings, you can find all that and more at the PPI website” Thanks @hot_rod.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Instead of going solely by Pex-A, Pex-B, and Expandable Pex-B, go by the standard they meet.
F1807, F1960, F2080, F2159, etc… It will be listed on the pex and fitting.
Then match the fitting/joining method to the standard of the pex. Some pex tubing meet multiple standards like the sioux powerpex- meaning you can use multiple joining methods.
Each fitting will only have one standard method of joining, meaning you can't use F1807 crimp method on F1960 expansion fittings. Nor can you use F1960 expansion fittings with F2080 expansion method (rehau).
Just match the standards and you won't have an issue.
1 -
the method of crosslinking determines the flexibility of the pex tube. It questionable in my mind if the B pex can tolerate expansion?
Are Zurn and Sioux chief the only brands promoting expanding B pex?
There are a number of online videos showing the tube splitting after expansion
Time will tell how well the B pex expansion pans out.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Definitely questionable as the explanation for it is "through meticulous enhancements" per Zurn.
I'm sure there's some tech sheet out there explaining in detail why this new type B pex is now expandable.
Sioux chief retroactively approved their powerpex b for expansion. Stating any pex-b dated 2018 onwards will be approved for expansion. Maybe they were waiting for testing and approval process? They put a 25 year warranty on it and must be expanded using a self-rotating head.
Anyway, I'd agree and stay safe with using pex-a for expansion.
1 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements