Pitching exhaust towards termination.
I recently installed a new IBC boiler. I failed inspection on the venting. Because of the location of the unit and the house being finished I had to run the venting up and then down to its final termination. I left no bellies in the pipe for condensate to accumulate but it's not exactly to the manufacturers recommendation. I don't understand what could possibly happen. Sure you will have water dripping out of the exhaust pipe. But other than that what's the problem. I've had the unit installed for a month now and no error codes. I've done this before no call back. I'm in San Francisco California and no chance of freezing weather. Please some show me the light or tell me I've broken the matrix.
Comments
-
Bottom line, if it failed inspection and your installation is not in accordance with the manufacturer's requirements… you're stuck.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
All boilers are supposed to be installed to the vent slopes up from the boiler. They want the condensate to run back to the boiler to drain.
They are not going to re right the boiler manuals or codes just because you live in an area not subject to freezing.
The MFG install instructions take precedence over any local codes
0 -
You are correct, mechanically it will work fine sloping out. I have done it and we have freezing temperatures. (As long as the location of the block of ice below the exhaust doesn't bother anybody!) But yes, inspection is inspection. In my area, inspectors seem to spend very little time on boilers unless it is a commercial application.
0 -
Always best to check all pertinent information before installing. That way, you get paid. If the equipment doesn't
fit the application, modifications may be needed to the structure or system relocated to another area.
Sometimes it can't be done.
0 -
-
that condensate running back to the boiler helps keep the HX surfaces clean. It runs across the surfaces to get down to the condensate drain.
Depending on operating temperature and hours if run time, you could have a bit of water to deal with outside
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements