Gas furnace consumption

camiarrobino
camiarrobino Member Posts: 83
I had a 60k BTU 96% Trane furnace installed. Considering a therm of natural gas is 100,000 BTU, if this furnace runs for 1 hour, will I consume 0.6 therms of natural gas?
Mad Dog_2

Comments

  • mattmia2
    mattmia2 Member Posts: 10,845
    yes, if it is single stage. it probably is multi stage or modulating so it will consume less if controlled properly
    Mad Dog_2
  • camiarrobino
    camiarrobino Member Posts: 83
    mattmia2 said:

    yes, if it is single stage. it probably is multi stage or modulating so it will consume less if controlled properly

    I believe it is just single stage. It's an A951
    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,400
    It will burn .6 therms in an hour if the gas is burning for the entire time.
    Mad Dog_2
  • pecmsg
    pecmsg Member Posts: 5,282

    I had a 60k BTU 96% Trane furnace installed. Considering a therm of natural gas is 100,000 BTU, if this furnace runs for 1 hour, will I consume 0.6 therms of natural gas?

    That furnace will only run nonstop when at or below design conditions. Thats only 2 or 3% of the total time its operating.
  • Mustangman
    Mustangman Member Posts: 113
    Is this natural gas? If so, you can clock your gas meter and find out how many BTUs you are using. Its pretty simple to do. You need to use your stop watch app on your phone.Find the cubic foot dial. Turn the stat way up. See how many seconds it takes to burn one cubic foot. Lets say it took 44 seconds.
    3600 sec in an hour 3600 x 1 cubic foot= 3600 divided by the 44 seconds = 81.82. There are 1050 BTUs per cubic foot of gas sooo 81.82 is the cubic feet of gas burned in one hour x 1050 BTUs = 85,911 Input. This is a great tool. If there is a question about the boiler producing what it should, this little bit of math will save your butt.
    Steve
    bburd
  • captainco
    captainco Member Posts: 796
    If left at factory settings its input is probably lower
    mattmia2WMno57
  • GGross
    GGross Member Posts: 1,258
    He's got a good point, our "70k" furnaces as they are labeled are actually 66,000 BTU input for example.
    WMno57